Broncosaurs (Customer) asked a question.

GS20-PID-Analog IN Scaling

Is there a way to scale the analog in to read in user units. I need to control a blower to SP of 1.2 PSI. GS20 with a 0-10vdc PTD25 transducer for the feedback. I would like to read the transducer in PSI and have the PID SP also in PSI.

 

P00.25 I can change the units and decimal, PSI:01Ch, .000: 0003h or 451d

All the scaling using the P03.xx is to scale voltage to frequency.

 

0VDC = 0 PSI, 10VDC = 15 PSI

 

Thanks Brad


  • ADC_DriveMotorsLSPLC_PM (AutomationDirect)

    use the following parameters:

    P00.04= 10 (PID feedback will show as b on the user defined display)

    P00.25 = 1C2hex (sets PSI and decimal)

    P00.26= 15 (sets 15 PSI scale)

    P03.00 = 5 (sets PID Feedback for analog input 1)

    P08.00 = 1 (enable PID

     

    this should be what you need. I highly recommend use of the GS4-KPD to see the user units. On the GS20 display, you will see F1.20 for the setpoint and b1.20 as the feedback.

    Expand Post
    • GS4kpd