CLICK PLC C0-01DD1-D

Hello, I am new to PLC and HMI programming.

Can you help me connect my Click C0-01DD1-D PLC and Kinco GL070E HMI. PLC programming is ok, HMI programming ok, but I can't control my PLC from my HMI.

I'm using the RS232 cable.

I thank you in advance.

NDD


  • Adisharr (Customer)

    You'll need to use Modbus RTU as I don't se a Click specific protocol. For RS232, use com 2 and make sure Modbus is selected as the port setup (default).

     

    Check your cable pin out and ensure the following:

     

    HMI RxD goes to PLC TxD

    HMI TxD goes to PLC RxD

    HMI 0V goes to PLC 0V

     

    The baud rate, parity and stop bits need to match between devices. The HMI will be the master and the PLC the slave. I forget if the master is automatically node address 1 so just in case it is, set the PLC node address to 2.

     

    You can view the Modbus addresses in the PLC through the address picker. Typically MODBUS 984 addressing is used.

     

    All Modbus registers are 16 bits. For 32 bit access, two are used usually sequentially.

     

    Example: PLC address DS1 (also a 16 bit integer) = Modbus address 400001, DS2 = 400002

     

    PLC address DD1 (32 bit integer) = Modbus address 416385 and 416386. The HMI will know to use both addresses as long as you specifiy the first address and that it is to be viewed / treated as a 32 bit integer.

     

    Floats can also be used (data will just be stored in that format)

     

    I would create a data view element in your HMI for address DS1 and then try and read / write to that.

     

    Hope that helps a bit :)

     

     

    Expand Post
  • kewakl (Customer)

    Also, as is the case with modbus, if the received values are not as expected, try adding/subtracting ONE from the register address.

  • frdicky (Customer)

    Thank you very much guys for your answers, I'm doing the test today and I'll let you know for the rest.