Eric R (Customer) asked a question.
Current Rating for Relay
Slim Interface Relays (automationdirect.com)
KPR-SCE-24VACDC-1
The output current rating is listed as: 6A @ 230 V in the tech spec sheet above.
I'm a noob. Is it rated 12A @ 115 V or just 6A?
6A only, if the component needs more current then you would have to get another contactor or relay that can handle the current and voltage needed
Thank you for the reply. The fan motors I plan on running are small ( rated 4 A total ). But I read in the reviews that these relays should be derated for "motor loads" to 20% rating ( 1.2 A ). I was just going to wire 3 of these relays in parallel ( to get in the ball park ) as I could not find a 24V AC Coil that was higher rated and has sufficient internal resistance for the signal circuit ( Based on the < 0.2 VA power consumption rating these appear to have large internal signal circuit resistance - around 2800 Ohms?). If I am out of line, tell me. I'm not an electrical engineer.
True they are derated, but I think your small fan motor should be fine. Do you know the HP rating of the fan motor?
Use a 781-1C-24D relay and a 781-1C-SKT socket. It is rated to 15A @ 230V
This seems far superior to the "work around" I had planned... Do you know if these need to be derated for " motor loads as well?
those come in 1,2, or 3 pole and have been working great for me on my projects
This one has 24v AC coil like you said you needed, and 15A load rating, wich has a derating high enough for your 2.2A loads. Capable of 1/2HP load across the contact poles at 120v AC:
https://www.automationdirect.com/adc/shopping/catalog/relays_-z-_timers/electro-mechanical_relays/square_-z-_cube_relays,_plug-in,_3a_-_15a_(78x-z-_qxx-z-h78x_series)/general_purpose,_15a_(781_-z-_782_-z-_783_-z-_784_series)/783-3c-24a
The coil resistance is "only" 110ohms though. Do you know for sure you need kohm+ resistance? How come? The high resistance coils all seem to be higher voltage models according to the spec sheet for these series.
The coil resistance is "only" 110ohms though. Do you know for sure you need kohm+ resistance? How come? The high resistance coils all seem to be higher voltage models according to the spec sheet for these series.
I think I need the high resistance for a few reasons:
What VA rating is your control transformer?
This relay says it consumes 3VA of power for the coil for all models coil voltage and has a rating of 1/3 HP load which you are well under:
https://www.automationdirect.com/adc/shopping/catalog/relays_-z-_timers/electro-mechanical_relays/octal_relays,_plug-in,_10a_-_16a_(750r_-z-_h750_-z-_755_series)/general_purpose,_10a_(750r_series)/750r-3c-24a
That first relay I linked earlier says it draws 2.05 watts at 24v coil. If we divide watts by voltage we get .085 amps load. Feed that into a VA calculator and I get 2VA load for the coil.