AkaHammer (Customer) asked a question.
Why so many errors? 300 reads with like 230 errors???
I have this working but lots of errors returned by MRX instruction using SP117 to a counter(SP117 port Comm error).
DL06 Port 2 setup:
Modbus
timeout =x1
RTS on delay=0 ms
RTS off delay=0 ms
addresses=1&2
Baud=19200
Stop bits=1
Parity=Odd
Shielded cable to VFD
15 pin connector wired like manual page K-3 (RS485-2 wire)
Termination resistor used on board drive
Ladder Logic interlock between two MRX instructions like manual page 4-28 (two drives)
Tried like everything basically same result?? Tried slow down in program, slow down baud rate, different RTS delays etc..??
Yaskawa E7 Drives setup:
H5-01=addresses=1&2
H5-02=baud=19200
H5-03=parity=odd
H5-04=alarm only don't stop drive on comm. error
H5-05=comm time out disabled
H5-06=drive transmit wait time=5ms
H5-07=RTS=On (must be on for RS485-2 wire per Yaskawa manual)
H5-08=Modbus
H5-09=comm. error= 2 seconds
Additional info:
DL06 connected via ethernet to CMore
4 Plc's do ethernet reads from this DL06 every 1 second
Could the burden of the ethernet comms be affecting serial comms???
Any idea's or comments are welcome again, I have checked everything like 20 times and tried all different kinds of settings.
Thanks in advance for any help
I had one system among several duplex pump stations that would give many errors when one or both VFDs were running. I ended up terminating the shield to ground in both drives as well as the main control panel to solve it. The RS422 wiring for a P1000 is documented that way and I was using P1000 drives.