bskeebers (Customer) asked a question.
Hello,
This may be a total n00b question, but I have 3 separate devices that all require AC input power:
-P301AC to power my Productivity3000 5-slot base
-PSE24-160 to provide 24 VDC to various field devices
-PSE12-230 to provide 12 VDC to various field devices
What is the best way to route the input power for these modules? I typically use power distribution blocks (i.e. busbars) for DC power but am not seeing any busbars that state that they are rated for AC.
I'm aware I should be running each live wire through a circuit breaker before feeding into the AC modules, but how do I split the power upstream from that? I have a single 120 VAC line coming into the control cabinet that I'd like to use to power these three (my current needs are minimal, I just need access to both 12 VDC and 24 VDC).
Any guidance would be greatly appreciated.
I do same as PouchesInc for the 120 VAC and 24 VDC to terminal blocks and jumpers to make several connections available, I try to keep it so only one wire per terminal so lots of connections available for like sensors, neutrals etc.. Heavier loads of 120 VAC power distribution blocks(rare thing). I like terminals that have the screw jumpers with strip, not plug in jumpers, had issues with those. And prefer spring terminals so they don't come loose with vibration where as screw terminal do just that, then occasionally tighten the screws on jumpers or if any weird things happen tighten all the jumpers again because with vibration and heating and cooling they have been known to work loose
Last few years anything 480 VAC 3 phase I have been using Manual motor circuit protectors with line side busbar system, did not like this at first, but if done properly it is great.
additionally I put barriers easily recognizable in terminal strips to separate the 120 from 24 volts, and color code for terminals.
Again last few years started using fuse holders that can be bus bared together rather than power distribution blocks. Like Automation Direct fuse holder part # EHCC1DU-12 and busbar example part# EB1P100M15 and tap block to feed main power to busbar system part# EPWR1PLP-1
Also use red wire for 120 vac control wires and blue wire for 24 vdc/ blue and white for 24 vdc com, and black for 480 vac 3 phase. Also green with yellow stripe for grounds and always put a lot of these.
These things to me are good practice and make it easy to look at a panel and see what is going on quickly.