Camilo (Customer) asked a question.

I have had problems connecting my plc click plus via ethernet with a Weintek HMI. I would like to know if you have any reference or guide on how to do it. Thank you.

  • ADC Community_02 (Automationdirect.com)

    hey @Garry (Customer)​ in Click version 3.10 we disabled port 25425. 

    Release Notes:

     

    2) Improved Security by disabling external communications of 3rd party HMIs using the proprietary programming port on UDP 25425. These devices should be reconfigured to use Modbus TCP 502. 

     

    This open port was a security issue for CLICK PLUS so we had to close it. It was a proprietary programming port that Weintek was using, so closing it makes that connection guide out of date.

     

    The Click V3 modbus driver uses port 502:

    http://dl.weintek.com/public/PLC_Connect_Guide/KOYO_CLICK_V3_MODBUS_TCP_IP.pdf

     

     