Looking on how to program a low level cutout for a pump pulling water from a tank. Have an analog sensor in the tank. I’m thinking using > or > something along those lines.

Ssparky (Customer) asked a question.
Looking on how to program a low level cutout for a pump pulling water from a tank. Have an analog sensor in the tank. I’m thinking using > or > something along those lines.
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
Hi @Ssparky (Customer)
Can you tell us what PLC you are using?
You are correct in thinking about using the comparison instructions in the program.
Thanks,
Garry
https://accautomation.ca/series/click-plc/
https://accautomation.ca/series/brx-do-more-plc/
https://accautomation.ca/series/productivity-1000-plc/
Here is a Click example. In my case, the tank is a remote PLC but the principle is the same. I have separate subroutine where I map the C15 bit to the actual output. I use SET and RESET instructions so that the state of the fill operation is retained in the event of a power cycle or program download. I use debounce timers to make sure the tank level truly is at or beyond the setpoint and not just a blip of the transmitter signal caused by noise or someone briefly opening a sample port. I also have a separate alarm subroutine that checks the health of my 4 to 20mA sensor and sets the alarm T48 if that signal is out of range for a couple of seconds. That alarm will also stop the fill cycle.