• z28z34man (Customer)

    in a round about way yes but you will need a program in the P1000 to map EIP data to IO

  • Rob (Customer)

    Would that be similar to Producer/consumer tags? I'm not sure I know what EIP data is.

  • z28z34man (Customer)

    Not quite the same thing as the setup is a bit different.

     

    I would set up Ethernet IP implicit communications between the productivity and a logix PLC where the productivity is the IO adapter and the AB is the scanner. i have done this several times between a control logix and a productivity but normally it is just to pass data

     

    https://www.youtube.com/watch?v=FNGIgqi0AYQ

    Expand Post
  • Rob (Customer)

    Thanks form your input. We will look at that if/when we attempt to implement this type of system. We are considering using this scheme as a sort of Cell control setup, with the P-5XX controllers communicating their data back to a Micro/Control Logix.