ADC_HMI_PE (AutomationDirect) asked a question.
https://www.automationdirect.com/support/software-downloads?itemcode=CLICK
Improvements
- Password requirement for Ethernet CPUs can now be disabled.
- Improved Security by disabling external communications of 3rd party HMIs using the proprietary programming port on UDP 25425. These devices should be reconfigured to use ModbusTCP 502.
- Added a new method for C0-1x and C2-x CPUs to Reset to Factory Default using the RUN-STOP switch. Power up in STOP mode, then RUN-STOP three times before 30 seconds expires.
- Added new System Data Registers for the MAC addresses of Port1 (SD188-SD193) and WLAN (SD194-SD199).
Fixed Bugs
Software
- MQTT Server Name field was improperly limiting the URL to 4 levels.
- Fixed issue with Export CLICK Loader File which caused "Failed! ErrID = 4".
- Fixed issue with CLICK Project Loader which could cause the PLC to lose its firmware.
- The Instruction Menu in Ribbon mode was inserting a Receive instruction for the Send icon.
Firmware
- COPY instruction of DF and DD in Copy Binary mode was operating as Copy Value mode.
- Improved reliability of project transfers which sometimes caused, "Error (-7): Write error" and "GUI-030 Transfer Failed".
Found the reason of the problem:
Improved Security by disabling external communications of 3rd party HMIs using the proprietary programming port on UDP 25425. These devices should be reconfgured to use ModbusTCP 502.
The device type of the click PLC must be changed to the new v3 model in the Weintek program.
Regards,
Hans