mariothe1 (Customer) asked a question.
hello new to forum using a DL 260 CPU with a ERM Communication module to a remote base EBC The trouble is I cannot force a input on the remote bass I can force Control bit and I'll put but not inputs I can force inputs on the Master bass
I am running DS 5
https://support.automationdirect.com/faq/faq_group.php?product_id=4
The D2-240, D2-250, D2-250-1 & D2-260 CPUs support bit override.
The D2-230 does not support override.
You must use a K-Sequence or Ethernet Link to use overrides, a DirectNet link will not support overrides
You can also turn bits on or off with Data View for a single scan to trigger events, but the PLC will update the image register on the next scan. The inputs will reflect their actual state and the outputs will be the result of the rung that controls them.
REMEMBER:
If you leave an override bit enabled and return the machine to service it is still in the bit override mode.
Be sure to turn override bits off before returning the PLC to service.
The above may help you out.
Regards,
Garry
https://accautomation.ca/
Reminder that FAQ's that are on the store now reside in the community knowledge base:
https://community.automationdirect.com/s/article/FAQ-DL205-How-can-I-override-inputs-and-outputs-in-my-DL205-1581003816798
thank you for your time I must be doing something wrong because it still doesn't work on remote base
thank you for the time I tried that but it still does not work on remote base works master bass
Coming from A/B to Directsoft, I ran into similar confusion. In A/B parlance "forces" is most similar to what Directsoft calls "Overrides". Your screen shot shows a data view which will let you write a value to a memory location, which is not the same as forcing. It would be like opening up a data table in RSLogix and typing in a new value for a bit.
If that memory location is also a real world I/O address the status will immediately be overwritten by the real input status in the case of an input address, or by your PLC code if any exists and is running in the case of an output.
Go to the DirectSoft top menu, click PLC > Setup > Overrides.
On that dialog box you can enter the addresses you want to force (override) and then enable the overrides there.
thank you all but there's still something wrong still can't force or override input in slave rack
I can Force inputs on in master Rech