NHRider (Customer) asked a question.
Circuit Breaker Descriptions and SCCR ratings
Many of your circuit breaker descriptions show an SCCR(e.g. FAZ-B63-3-NA). This bothers me a bit since neither fuses nor circuit breakers have SCCR ratings. They have interrupt ratings. This is significant when determining panel SCCR. It would be nice to see those descriptions updated to not say SCCR. Thanks.
Thanks for your feedback! I have forwarded your suggestion to the Power & Circuit Protection Product Manager.
You are correct. Fuses and circuit breakers have interrupting ratings. Contactors, terminal blocks and bus bars have SCCR. However, both ratings are used the same to calculate SCCR for the entire enclosure. UL 508A Table SB4.1 use SCCR (Short circuit Current Rating) to describe all of these the same.
Thanks,
Leon Kenison
Automatrix, Inc.
Senior Controls Engineer