C-more 9 & ATV71
Will the C-more 9 or the EA7 communicate with a Schnieder ATV71 drive? I don't see it listed but...that means nothing.

Tom@Pton (Customer) asked a question.
Will the C-more 9 or the EA7 communicate with a Schnieder ATV71 drive? I don't see it listed but...that means nothing.
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
Hi Tom@Pton,
The Schnieder ATV71 drive has Modbus protocol as standard. This means that the C-More with the Modbus driver will communicate.
Modbus RTU serial is standard on the drive. Modbus TCP looks like an external adapter is required.
https://www.se.com/ca/en/download/document/1755863/
Regards,
Garry
https://accautomation.ca/series/c-more-hmi-series-panel/
Thanks.
I asked my wholesaler for some info on an Ethernet card. The answer was well, maybe, but probably not likely. I t may be easier to use I/O for no more than what I have in mind.
Thanks for the update, Tom.
Garry