Bolt (Customer) asked a question.
I have an existing Click system, with a C0-11DRE-D CPU, and a few input and output and analog modules, 4 total. I am trying to add 2 new modules, a relay output and an input module. I have done this before on many systems, but this time I am struggling.
I put the CPU in STOP, powered down all 24VDC to the CPU and modules, and plugged in my 2 new modules, latching them securely.
Re-applied 24VDC, left CPU in STOP, went to PC to try and setup the configuration. I can add the 2 new modules in the System Configuration (only when disconnected from PLC), connect to PLC, write to PLC, and upon going back to System Configuration it informs me that the PLC(ONLINE) has no modules in the 5 and 6 slots.
Same occurs if I put the CPU in RUN position, and try to write (in STOP mode) the new configuration does not take.
Please advise. I am still using Programming Software version 2.30. Not about to change firmwares in the middle of this task.
The Click modules are pretty cheaply made and I've had a couple of the bus connectors come loose when attaching modules. Check to make sure they are held in place by the module enclosure.