CTT - all models

Can we get an option for the CTT timer mode to retain the elapsed time through a power down event? The START signal (or the RESET) signaling can clear the PV.

 

We currently use an obsolete timer that has PV retention. We need to know the elapsed process time in the event of a power outage. Our typical timer application is oven heating.

A reasonably priced UPS cannot sustain the heater load, so we cannot ride out sustained power interruptions.

 

I want the six digit display (hh.mm.ss) so the koyo timer is not an option.

 

Also, there is a typo in the revision history dates.

2nd edition is listed as 10/24

3rd edition is listed as 10/19


  • kewakl (Customer)

    Thanks Garry,

    I have not reached the bottom of that massive tome of a manual, yet.

    I will read about those modes.

    • Garry (Customer)

      The CTT does a lot of different modes.

       

      • kewakl (Customer)

        I think that I have devised an approximation of what I need.

        If I can, I will update tomorrow!

         

        Thank you, Garry!

         

        [edit add picture]

        CTT-Retentive with start_stop_reset

        Expand Post