maciek (Customer) asked a question.November 7, 2020 at 9:53 PMhmi and simulatordoes the simulator work with a c more hmi Expand PostProductivity
Garry (Customer)6 years agoHi Maciek,The Productivity Simulator will only support Modbus TCP server/client connections on the external Ethernet port. You would have to select the Modbus TCP protocol on the C-More HMI for the connection to work.Regards,Garry Expand Post
kewakl (Customer)5 years agoI used Productivity Suite Ethernet for my sim/cmore test.Be sure to point your cmore to the IP address of the PC that is running the PAC Simulator Cmore 6.51PAC 3.8.0.14Expand Post
Gene Bond (Customer)5 years agoYes, what he said :) All I had to change from an existing C-More project to run from the Simulator instead of the Hardware was to set the PLC address as the PC address.Expand Post
Hi Maciek,
The Productivity Simulator will only support Modbus TCP server/client connections on the external Ethernet port. You would have to select the Modbus TCP protocol on the C-More HMI for the connection to work.
Regards,
Garry
I used Productivity Suite Ethernet for my sim/cmore test.
Be sure to point your cmore to the IP address of the PC that is running the PAC Simulator
Cmore 6.51
PAC 3.8.0.14
Yes, what he said :)
All I had to change from an existing C-More project to run from the Simulator instead of the Hardware was to set the PLC address as the PC address.