BE_ZERO_BE (Customer) asked a question.

Question about CLICK 4-20 mA output not working

I have a CLICK C0-02DR-D (PLC with analog I/O).

For verification testing, I connected a 500 Ohm resistor in series with an Ammeter between ACOM (analog common) and DA1 I.

I read no current while poking values into the analog output register (DF1 in this case).

Does the 4-20 mA output require an external loop power supply?

I could not find any wiring diagram in the hardware manual.

Thank you for your assistance.

 


  • BE_ZERO_BE (Customer)

    RBPLC - Thanks for the answer. That's what I was looking for.

    It seems odd that the information is in the catalog but not in the hardware manual.

    Best Regards,

    Bob in Poulsbo, WA