Elias20 (Customer) asked a question.

¿How can I read ASCII values ​​from a 4850 Stepper Drive with BRX PLC?

I am communicating with the drive through 232 and so far I have apparently been able to write values ​​such as Electronic Gear to the drive, but I also want to read that same value from the drive to see if it really made the change, I know it is with the Stream In function but I don't know how to configure the instruction to read values ​​like Electronic Gear or Acceleration

 


  • ADC_PLC_ENG (AutomationDirect)

    You have to use a Streamout with the SCL command for the parameter you wish to read (ex. EG for electronic gearing) without a numeric value. The you must enable the Streamin instruction to capture the response from the drive.

  • Garry (Customer)

    After your Streamout command, use the On Success, Set Bit flag to trigger the Streamin instruction.

    Here is an example of using Streamout/Streamin. It is for serial (Modbus ASCII) communication, but you can get the idea of the logic.

    https://accautomation.ca/brx-do-more-plc-modbus-ascii-protocol/

    I hope this helps you out Elias20.

    Regards,

    Garry

    Expand Post