Should I directly connect solenoid valves to PLC digital output?

For example, I see this

Should I directly connect solenoid valves to PLC digital output?

Thanks

 

Capture11

 


  • If there is a short you'll burn up the output. So you'll want to either fuse it or use a relay. I like the RS4N-DE slim card relays for I/O isolation. Just stick to the 4 relay version. The 6 relay modules are worthless.

    Selected as Best
  • Garry (Customer)

    Hi Marco,

    DC solenoids have surges that can destroy PLC outputs. The information that you specified indicates that the Nitra solenoid valve has a surge suppression diode. This is good.

    I would just verify the current ratings for the solenoid and the maximum per common point on the PLC output.

    Regards,

    Garry

  • If there is a short you'll burn up the output. So you'll want to either fuse it or use a relay. I like the RS4N-DE slim card relays for I/O isolation. Just stick to the 4 relay version. The 6 relay modules are worthless.

    Selected as Best
  • ssweber (Customer)

    I also like the RS4N-DE for higher amp needs, but also have had good luck using the 8-pt Click digital Sourcing outputs (.3amps) to directly power any of the AVS directional solenoids. I put a 1n4004 diode directly at the solenoid, between the +/-. Haven’t had any fried cards.