Marco (Customer) asked a question.
For example, I see this
Should I directly connect solenoid valves to PLC digital output?
Thanks

Marco (Customer) asked a question.
For example, I see this
Should I directly connect solenoid valves to PLC digital output?
Thanks
Hi Marco,
DC solenoids have surges that can destroy PLC outputs. The information that you specified indicates that the Nitra solenoid valve has a surge suppression diode. This is good.
I would just verify the current ratings for the solenoid and the maximum per common point on the PLC output.
Regards,
Garry

If there is a short you'll burn up the output. So you'll want to either fuse it or use a relay. I like the RS4N-DE slim card relays for I/O isolation. Just stick to the 4 relay version. The 6 relay modules are worthless.

I also like the RS4N-DE for higher amp needs, but also have had good luck using the 8-pt Click digital Sourcing outputs (.3amps) to directly power any of the AVS directional solenoids. I put a 1n4004 diode directly at the solenoid, between the +/-. Haven’t had any fried cards.