WilK (Customer) asked a question.

Click PID manual/auto switching

I'm running into the problem setting up multiple PID's.

It seems that no matter what address block is used for each PID, every second PID loop that is entered does not switch into Auto mode, also the alarm settings are disabled.

I.e. PID001, PID003, PID005, PID007 works fine

but PID002, PID004, PID006, PID008 will not swich into AUTO mode.

All PID's setup the same with and consecutive Parameter areas.

Changing parameter areas does not help.

After deleting PID's 2,4,6,8, PID's 1,3,5,7 still work fine.

I don't know if this is a PLC or programming software issue.


  • WilK (Customer)

    Thanks for your quick response.

    No I did not use the "Find Avail...".

    I started with C200, DS200, DF200 for the first PID Loop, all other PID's memory blocks after that.

    At this point it was a test of the problem. There was no Ladder program, just an END statement in Rung 1

    • WilK (Customer)

      Garry, thanks for your response.
      I was out of town yesreday.
      I loaded and run your test program and it worked fine.
      I attached my program which is the same except my address block range starts at 200.
      It has the problem not working on every other loop.
      Thanks
      Wil


      PID Loop C DS DF
      PID001 200 200 200
      PID002 240 215 225
      PID003 280 230 250
      PID004 320 245 275
      PID005 360 260 300
      PID006 400 275 325
      PID007 440 290 350
      PID008 480 305 375
      Expand Post
  • Garry (Customer)

    I'll let someone from AD respond to this. It looks like everything should work.

    Regards,

    Garry

  • ADC_HMI_PE (AutomationDirect)

    I think I see the issue.

     

    Are you looking at the Mode in the PID Monitor? If I put in two PID loops, the second loop does not indicate it is in Auto Mode in the PID Monitor. But if I look at the DataView, the PID AutoMode Indicator bit is high indicating it is in Auto Mode.

     

    This looks like a bug in the PID Monitor.

     

    CLICK PID Auto Mode

    Expand Post
    • WilK (Customer)

      I use the PID monitor.I think the problem has to be in the assignment of the address blocks.Two consecutive blocks don't work starting with C, DS, DF 200.
      -------- Original message --------From: Community Admin <
      communitymod@automationdirect.com> Date: 9/10/20 16:28 (GMT-05:00) To: wkantus@gmail.com Subject: ADC_HMI_CLICK_PE answered you: Click PID manual/auto switching

      @media only screen and (max-device-width: 480px) {
      html { -webkit-text-size-adjust: 100%; }
      table.container { width: 100% !important; }
      .hidden-for-mobile { display: none !important; }
      .callToAction, .callToAction td, .footer {
      font-size: 12px !important;
      }
      .button .text { font-size: 12px !important; }
      .defaultIndentation { width: 10 !important; }
      .text { font-size: 12px !important; }
      a.button { width: 96 !important; }
      a.buttonWide { width: 118 !important; }
      a.buttonAuto { padding-left:1em !important; padding-right:1em !important;}
      a.button, a.buttonWide, a.buttonAuto {
      height: 23 !important;
      line-height: 23px !important;
      border-radius: 4px !important;
      -webkit-border-radius: 4px !important;
      -moz-border-radius: 4px !important;
      }
      td.buttonWrapper {
      width: 98 !important;
      height: 23 !important;
      }
      img { display: inline !important; }
      .circle { border-radius: 50%; clip-path: circle(50px at center); }
      .square { border-radius: 10%; clip-path: circle(10px at center); }
      }
      @media only screen and (min-device-width: 600px) {
      table.container { width: 600px !important; }
      }
      @media screen {
      @font-face {
      font-family: 'Salesforce Sans';
      font-style: normal;
      src: local('Salesforce Sans'), local('SalesforceSans'), url(
      https://community.automationdirect.com/fonts/SalesforceSans/SalesforceSans-Regular.woff) format('woff');
      }
      }
      a, a:visited { color:
      #015BA7; text-decoration:none; }
      img { display: block; }
      .preheader { display: none !important; }
      table {
      border-collapse: collapse;
      mso-table-lspace: 0px;
      mso-table-rspace: 0px;
      }

      I think I see the issue.
       
      Are you looking at the Mode in the PID Monitor? If I put in two PID loops, the second loop does not indicate it is in Auto Mode in the PID Monitor. But if I look at the DataView, the PID AutoMode Indicator bit is high indicating it is in Auto Mode.
       
      This looks like a bug in the PID Monitor.
       

      [Image: CLICK PID Auto Mode]

       
       











       
       



       




       


      ADC_HMI_CLICK_PE (AutomationDirect)






      I think I see the issue.  Are you looking at the Mode in the PID Monitor? If I put in two PID loops, the second loop does not indicate it is in Auto Mode in the PID Monitor. But if I look at the DataView, the PID AutoMode Indicator bit is high indicating it is in Auto Mode. This looks like a bug in the PID Monitor.  CLICK PID Auto Mode

       








      View/Answer




        or reply to this email








       



       


       
       
       

       




      Replying to




       



       




       


      WilK (Customer) asked a question.




      Wednesday, September 2, 2020 1:20 PM








      Click PID manual/auto switchingI'm running into the problem setting up multiple PID'
      s.It seems that no matter what address block is used for each PID, every second PID loop that is entered does not switch into Auto mode, also the alarm settings are disabled.I.e. PID001, PID003, PID005, PID007 works finebut PID002, PID004, PID006, PID008 will not swich into AUTO mode.All PID's setup the same with and consecutive Parameter areas.Changing parameter areas does not help.After deleting PID's 2,4,6,8, PID's 1,3,5,7 still work fine. I don't know if this is a PLC or programming software issue.


       





       



       



       





       


       






       


      ADC_HMI_CLICK_PE (AutomationDirect)


      I think I see the issue.  Are you looking at the Mode in the PID Monitor? If I put in two PID loops, the second loop does not indicate it is in Auto Mode in the PID Monitor. But if I look at the DataView, the PID AutoMode Indicator bit is high indicating it is in Auto Mode. This looks like a bug in the PID Monitor.  CLICK PID Auto Mode