Garry (Customer) asked a question.

Click PLC Modbus ASCII Protocol

The Click can communicate Modbus ASCII to equipment.

Modbus is a communication method used for transmitting information over serial lines between electronic devices. The device requesting the information is called the Modbus Master (Client) and the devices supplying information are Modbus Slaves (Servers). This protocol was originally developed by Modicon systems.

Modbus protocol comes in basically three different types. Ethernet (Modbus TCP) or Serial (Modbus RTU or Modbus ASCII). Modbus TCP and Modbus RTU come as standard protocols in the productivity series of PLCs.

We will connect the Click PLC to a Solo process temperature controller. This will be done using the Modbus ASCII protocol over serial RS485 communication wire. (Media) The present and set values (PV / SV) will be read from the Solo controller and the set value will be written when required. Let’s get started.

 

Click PLC Modbus ASCII Protocol

YouTube Video

 

Click PLC Modbus ASCII Protocol Solo 020-min

 

Regards,

Garry

 

https://accautomation.ca/series/click-plc/


kewakl and Garry like this.
  • ADC Community_02 (Automationdirect.com)

    As always thanks for your contributions to our community Garry!

    Selected as Best
  • ADC Community_02 (Automationdirect.com)

    As always thanks for your contributions to our community Garry!

    Selected as Best