Ac Drive speed control with PLC and Linear Transducer

Created Date: August 24,2019

Created By: Tflan

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I’m trying to keep the AC drive speed at 50% of a Linear Transducer using a Click PLC analog 0-10 output to the 0-10 v dc analog input on of the drive. The linear transducer is also 0-10 v dc. How would you right a program in Click PLC. The object is to match the line speed that can change so the motor speed can be faster or slower at 50% of the transducer.


  • adccommunitymod (AutomationDirect)

    Created Date: August 24,2019

    Created by: Tflan

    I’m trying to keep the AC drive speed at 50% of a Linear Transducer using a Click PLC analog 0-10 output to the 0-10 v dc analog input on of the drive. The linear transducer is also 0-10 v dc.

    How would you right a program in Click PLC. The object is to match the line speed that can change so the motor speed can be faster or slower at 50% of the transducer.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 24,2019

    Created by: RogerR

    To follow a 0-10v signal and use the feedback to stay in the middle range of the signal:

    Input the 0-10v input signal to a click tag.

    Multiply this tag with a scaling tag. Less than one would be slower, more than one would be faster.

    Output this new tag to the analog output to the drive.

    The min/max speeds in the drive will play a part as well.

    If this signal was a potentiometer on a dancer bar, adjusting the scale tag would position the dancer up or down.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 25,2019

    Created by: Tflan

    Than my you for your help.

  • adccommunitymod (AutomationDirect)

    Created Date: August 26,2019

    Created by: Tinker

    While it is not too clear on what the actual system configuration is, I'd imagine there is a some chance of instability and/or poor response with a simple proportional control. While one can certainly write one's own PID for a CLICK(it is not built in) I'd be inclined to recommend a Do-More BRX, not only does it have PID its ADC is considerably faster

  • adccommunitymod (AutomationDirect)

    Created Date: September 05,2019

    Created by: genebond

    The Accel/Decel of the drive makes a great Integrator :) The Proportional is done in as above. Who uses 'd ' 99% of the time anyway? :)