adccommunitymod (AutomationDirect) asked a question.

Speed control of 24 dc motor using a plc

Created Date: February 25,2008

Created By: krak

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

what is the best way to use a plc to control the speed of a 24 vdc motor?


  • adccommunitymod (AutomationDirect)

    Created Date: February 26,2008

    Created by: milldrone

    krak,

    You didn't mention the amp draw of the motor. But I'll take a stab at it any way.

    Dart makes a controller for motors up to 10 amps #65E10 you will need a 10 volt isolated analog output from the PLC. This presuming you have 24v DC power supply to work with.

    Then if your motor is less than three amps perhaps this little cutie will work for you. It's designed for driving direct drive analog DC coils up to 3 amps. but should work on a motor also. And a isolated 10 volt analog output is not needed. http://www.pwmcontrols.com/

    Vaughn

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 26,2008

    Created by: Merzo59

    Use a DRV102 PWM Driver. It's a piece of cake to use and only costs $7.00. I use it to control a +12VDC motor..

  • adccommunitymod (AutomationDirect)

    Created Date: April 04,2008

    Created by: Adisharr

    I tend to favor the drive method myself (such as the DART unit already mentioned). Unless you really like playing with integrated circuits or the cost has to be kept at an absolute minimum, you 're better off w/ a complete drive. K-B Electronics also makes some decent drives.

    A quick call to either Mfg. can solve your problem.

  • adccommunitymod (AutomationDirect)

    Created Date: February 25,2008

    Created by: krak

    what is the best way to use a plc to control the speed of a 24 vdc motor?