ea7 to DL06 ethernet connection

Created Date: January 14,2018

Created By: murrayt57

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am trying to get a cmore ea7 connect over Ethernet connection to my DL06 plc that resides at 192.168.0.20. I have tried a lot of setups but none work. Can some one guide me that proper procedure to do this? My connection has a router so there are no crossover cables.


  • adccommunitymod (AutomationDirect)

    Created Date: January 14,2018

    Created by: murrayt57

    I am trying to get a cmore ea7 connect over Ethernet connection to my DL06 plc that resides at 192.168.0.20. I have tried a lot of setups but none work. Can some one guide me that proper procedure to do this? My connection has a router so there are no crossover cables.

  • adccommunitymod (AutomationDirect)

    Created Date: January 15,2018

    Created by: mwdkmpr

    Make sure your panel IP is on the same subnet as the PLC. 192.168.0.###

    Are they on the same LAN?

    I assume you have selected the DL Ethernet driver and entered the PLC IP address in the panel manager.

  • adccommunitymod (AutomationDirect)

    Created Date: January 15,2018

    Created by: franji1

    Make sure your subnet mask is valid also for both the panel and the ECOM. Should be something like 255.255.255.0 or 255.255.0.0 or 255.255.252.0 or ...

  • adccommunitymod (AutomationDirect)

    Created Date: January 16,2018

    Created by: murrayt57

    thank you for the responses. My problem is solved by the help of tech support. I was just not configuring the proper ip for the cmore screen.