adccommunitymod (AutomationDirect) asked a question.
Created Date: March 16,2017
Created By: LesKlar
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
After searching here and across the internet, I find that there is little detailed information about this subject. Here is my questions: 1) Is the DL205 system a good choice, and what CPU/control card is best? 2) I have an EA7-T15C color touchscreen. Is that a good choice? 3) Did see a bit of a forum discussion on Stage programming for this application vs. direct ladder logic, pros and cons? I am comfortable with both. 4) I am very familiar with the molding process and function of a molding machine. I have detailed electrical and hydraulic prints of the original control system. I also have a detailed OEM timing chart. What I do not have is access to any of the original program (I believe it was a Seimens controller). Any tips from anyone that has converted an injection molding machine to a new PLC controller? Thanks Les Klar
Created Date: March 16,2017
Created by: LesKlar
After searching here and across the internet, I find that there is little detailed information about this subject. Here is my questions:
1) Is the DL205 system a good choice, and what CPU/control card is best?
2) I have an EA7-T15C color touchscreen. Is that a good choice?
3) Did see a bit of a forum discussion on Stage programming for this application vs. direct ladder logic, pros and cons? I am comfortable with both.
4) I am very familiar with the molding process and function of a molding machine. I have detailed electrical and hydraulic prints of the original control system. I also have a detailed OEM timing chart. What I do not have is access to any of the original program (I believe it was a Seimens controller). Any tips from anyone that has converted an injection molding machine to a new PLC controller?
Thanks
Les Klar
Created Date: March 17,2017
Created by: plcnut
You said you have a timing chart. How fast does the response time need to be? are we talking milliseconds? or microseconds?
How many encoders? Or are the positions all analog?
Created Date: March 17,2017
Created by: jwbaker3
1) The 205 is a good platform, I would use the Do-More processor. I did a retrofit on 4 blow mold machines not too long ago. The Do-More nailed the temperature control auto tune the first try, controls +/- 1 degree F and the CPU scan time is much faster than the SLC that I replaced.
2) The EA7 is a good touch screen (If I were buying new I would use an EA9) I have install a lot of them (over 100) in customers plants. I have had 2 failures in the last 8 years or so 1 was a lightning hit and the other one had a surge on the Ethernet line from the ISP and took out the router, switches and the Ethernet port on the touch screen.
3) I prefer to write my code in Program blocks, Tasks and Stage. Now with DMD 2.0 you can use subroutines. They all have their place for program control and ease of following the logic. There are videos on the AD web site that will help with how and where to use each.
4) I know on the Blow mold machines temperature control is a big deal so I put each PID loop (22 zones) in it's own program block. I had the old logic so the conversion was fairly easy. I did add a lot of safety devices to bring the machine up to current code (not PLC related but a required part of the retrofit) and troubleshooting logic to the plc/touch screen to help the operators and maintenance.
JW
Created Date: March 17,2017
Created by: a agnone
LesKlar, keep us informed how it is going. that is a huge undertaking. We have over 60 molding machines. Each machine has many pages on the HMI with lots of setting on each page. Molding machines are very touchy piece of machinery. Would love to know how you are doing. It maybe something we might have to to down the road. And yes Seimens seems to be the plc in most of them.
Created Date: March 17,2017
Created by: pressgrove
The 205 should be fine. I haven't used the Do-More so I'll leave that input to others. I have used the P3000. It would also be a fine choice for this (as well as the P2000 I would assume). I 've done several with 405s. I only used that platform because of the 4 loop temperature control card that is available. I was pretty new to this and not having to deal with PID loops along with everything else was a bonus. Once we did one, we just stayed with the same platform.
EA7 is a fine choice, but agree with jwbaker3 that the EA9 is a better choice if for no other reason than support should last longer for it.
I did mine with ladder logic, because at the time Stage programming was a foreign to me. If I had to do it again, I would probably still use ladder. I used a lot of holding circuits in my logic just so the machine would drop out of cycle if certain safety limits were breached. Some hate holding circuits because they are harder to troubleshoot so I may get pushback from others on this comment.
You'll find that the OEM sequence/timing chart will be the most important thing you have. Some OEMs do it better than others.
Use the logic to control functions of the machine (i.e. control bits/relays) not the discrete outputs. Put the inputs and outputs in a separate section of logic, in another subroutine, etc. The general sequence of operations of most machines are the same. Doing this will allow you to reuse most of the logic for a different machine later, even if built by a different OEM.
Get a copy of ANSI/SPI B151.1-1997, Plastics machinery – Horizontal injection molding machines – Safety requirements for the manufacture, care, and use (or B151.29 for vertical machines). There are some very detailed standards regarding guarding, gate safeties, hydraulic safeties, mechanical (jamb bar) safeties, etc. and they can change depending on the tie bar spacing of the machine. If you 're familiar with injection molding machines, the standard is pretty easy to read.
I would install an SPI robot interface even if you don't have a robot on the machine. It's not that much more trouble and can save you a ton of hassle later if you decide to add one. Robot interfaces that aren't integrated well into the controls are a PITA to troubleshoot. The standard for this is SPI AN-116.
Created Date: March 17,2017
Created by: pressgrove
One other thing I thought of later... For run-off, I used the simplest mold I could find with no ejector rods installed. I used a small cylinder on a table with two end of stroke limits to work out the core sequences. That was by far the hardest part of the logic.
Created Date: March 20,2017
Created by: alchemist562
After searching here and across the internet, I find that there is little detailed information about this subject. Here is my questions:
1) Is the DL205 system a good choice, and what CPU/control card is best?
2) I have an EA7-T15C color touchscreen. Is that a good choice?
3) Did see a bit of a forum discussion on Stage programming for this application vs. direct ladder logic, pros and cons? I am comfortable with both.
4) I am very familiar with the molding process and function of a molding machine. I have detailed electrical and hydraulic prints of the original control system. I also have a detailed OEM timing chart. What I do not have is access to any of the original program (I believe it was a Seimens controller). Any tips from anyone that has converted an injection molding machine to a new PLC controller?
Thanks
Les Klar
what brand molding machine are you converting?
Created Date: March 22,2017
Created by: LesKlar
Thanks everyone for the tips. I am still putting together the proposal for management, so I will include the cost of a new EA9 15 inch screen.
To answer a few of the above questions and comments:
1) This is a Van Dorn 230 ton HT. This uses analog position sensors for the clamp, ejectors, and screw. Uses a proximity switch that counts rotations of the screw. The pressure and flow are handled by a couple of Rexroth amplifiers that require an analog signal to tell the amp the desired set point. The amps handle all the controls for feedback.
2) I am also planning on updating the safety circuits. Older machines rely on hardwired relays for the safety circuits. I am going to upgrade to modern dual channel safety relays. I also will be adding a few additional (required) safeties. For example, a redundant switch to monitor safety drop bar position.
3) The machine already has the SPI so this will be integrated into the retrofit. I have the SPI publications for the machine and the robot. I am also going to integrate a process monitor signal interface (RJG). This will allow easy hook-up of sequence signals that most second party monitoring equipment is looking for.
4) Pressgrove makes a very good point. I always separate the physical I/O into a separate routine or stage. It makes trouble shooting a lot easier.
5) I have a ladder logic program from a different machine (Mitsubishi PLC). This is not exactly going to transfer as the machine has a different hydraulic structure (uses a variable volume pump with a swash plate), but the basic sequence is the same.
I expect approval sometime next month, I put this as a month long planning and designing, and then 2 -3 weeks to implement (provided no parts are backordered). This means I should have a functional machine sometime in June. I will try to update this as I go, and I am sure to have questions.
The one area I have not had much experience in is temperature loops. I did a two channel set-up for a hot stamp machine, but this had a very fast heat/cool time so tuning was a snap. I read on this forum that some of the long heat times (typical of an injection molding machine) can be a beast to tune.
Thanks
Les Klar
Created Date: March 22,2017
Created by: plcnut
205 with a Do-more should be a great fit.
Created Date: March 22,2017
Created by: alchemist562
That's awesome. We have the same machine at our shop but its a 400 ton. We are starting to have problems with the S5 (always going into "pc in stop ") and we were thinking about doing the same thing. Only thing stopping me from pushing on with it is I do not have enough skill with analog programming from all the sensors and out to the valves. Hope it goes well for you. Hope you post updates and pics/vids of it.