I have analog input card F2-04AD-2, using an Ashcroft pressure transducer Range is 0/500psi, Input 1-5VDC, Supply 9-36VDC... The issue I am having is when the system has no pressure I am reading 819 in the PLC, so with my scaling it displaying 100psi on the panel... When I take the transducer and connect -V common with +V output I do read 500 on the panel, and 4095 in the PLC... at a complete loss, any help would be appreciated, thank you


  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: Tinker

    1-5V looks much like 4-20mA, they presumably don't start at zero so that open connections can be detected. You just need to subtract that 819 before you do your scaling, then you would scale for a 4V span (multiply by about 0.153)

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: jtak101

    1-5V looks much like 4-20mA, they presumably don't start at zero so that open connections can be detected. You just need to subtract that 819 before you do your scaling, then you would scale for a 4V span (multiply by about 0.153)

    Okay, so in my logic I now have:

    LD V2001

    MUL K500

    DIV 4095

    OUT V2012

    I am a little confused on the scaling for 4V span, The only way I scaled was with the psi rating, So If I understand what your are saying it would change to:

    LD V2001

    SUB 819

    MUL .153

    MUL K500

    DIV 4095

    OUT V2012

    Thanks for the response!

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: scott.lawrence

    you need to scale the transducer for your display.... is this from the other post?

    either way, the value you 're trying to get is 0-500, and the value you have is 0-4095.

    since you have a 250-1 processor, you can use an I-Box (SCALEB) to scale the input to your desired output.

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: jtak101

    you need to scale the transducer for your display.... is this from the other post?.

    Yes, this is a continuation of that, same application I resolved that thanks to your help I can now lock the highest pressure on the display

    since you have a 250-1 processor, you can use an I-Box (SCALEB) to scale the input to your desired output.

    I have never used the I-Box (SCALEB) function before, so is the math I have then is no longer needed? I will look into that I-Box function now.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: scott.lawrence

    the SCALEB is doing the math for you behind the scene , so to speak.

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: jtak101

    the SCALEB is doing the math for you behind the scene , so to speak.

    Okay so I can delete my math, then use the Ibox which I read the help menu so for my application would look like this?:

    Raw (12 bit binary) -- V2001

    High Engineering -- K4095

    Low Engineering -- K0

    Engineering Binary -- V2011

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: scott.lawrence

    raw is the location of the raw analog input.

    engineering units are the output you want, so in your case, the high/low would be 500/0 for the PSI of the device.

    engineering binary is where the scaled data will be placed.

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: jtak101

    I meant 500 on the engineering high units, okay perfect will put this in now and test it out, thank you... again!

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: Tinker

    you need to scale the transducer for your display.... is this from the other post?

    either way, the value you 're trying to get is 0-500, and the value you have is 0-4095.

    since you have a 250-1 processor, you can use an I-Box (SCALEB) to scale the input to your desired output.

    Actually, since the transducer is 1-5V I think he has an input of 819-4095 which he needs to scale to 0-500. I have not used Direct soft to any extent, certainly not the SCALEB, can it take a negative number for scale low? since 500/(5-1) = 125 per volt, I'd think that a scale low of -125 and scale high of 500 should give 0(psi) for 1 volt and 500(psi) for 5V ? a negative 125 psi would indicate an open circuit.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2016

    Created by: scott.lawrence

    Actually, since the transducer is 1-5V I think he has an input of 819-4095

    I didn't even catch that... but the SCALEB has In Min/Max as well as Out Min/Max that OP can enter 819-4095 for the In Min/Max, and 0-500 for the Out Min/Max