adccommunitymod (AutomationDirect) asked a question.
Created Date: July 29,2015
Created By: couv1
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have a PID loop setup using the DL06 processor and a F04AD2DA1 analog module. I have the output variable (V2205) set with a lower limit of 0 and an upper limit of 100. The loop seems to operate fine, except when it has a large span to gain (usually on initial start up). When there is a large span the output generally will hit the upper limit of 100. When the upper limit is reached the Loop Calculation Overflow error bit comes on (B2206.11) and the loop seems to stop executing. Sometimes the error will reset itself as the process variable gets closer to the setpoint, but more times than not the error stays on long after the process has passed the setpoint and the output variable is below the upper limit. Any ideas on how to clear this Loop Calculation Overflow error or how to avoid the error all together?
Created Date: July 29,2015
Created by: Do-more PE
Look at the Freeze Bias setting on the Tuning Tab.
Created Date: July 30,2015
Created by: couv1
It may be a while before I can run the system again. They are making mechanical changes. Looking at the Setup PID offline on the Tuning tab the Freeze Bias is not checked.
HI,
I have the exact same problem. Is someone have figure it out the way to solve this issue?
Thanks
Due to this is post being almost 8 years old. I would recommend you start a new thread.