adccommunitymod (AutomationDirect) asked a question.

Dl205 ??

Created Date: May 28,2015

Created By: ricowind

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Will the F2-04rtd work in expansion modules? Or does it have to be in the rack the CPU is


  • adccommunitymod (AutomationDirect)

    Created Date: May 28,2015

    Created by: bcarlton

    DL206 User Manual - Chapter 4 - Module Placement

  • adccommunitymod (AutomationDirect)

    Created Date: May 29,2015

    Created by: jwbaker3

    You may want to make sure you have a current firmware in the CPU. I had problems with one system we expanded were the CPU had been in service for years. After updating the firmware the analog worked fine. I think it was the combo card with the analog in and out on the same card, so it may not be an issue with the RTD card. But keeping the firmware up to date is still a good thing to do.

    JW

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 28,2015

    Created by: ricowind

    Will the F2-04rtd work in expansion modules?

    Or does it have to be in the rack the CPU is