adccommunitymod (AutomationDirect) asked a question.

DL06, GS3's and C-More Micro

Created Date: March 09,2014

Created By: wjones

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I would like to set up a 485 network to communicate with a DL006 (secondary port), a C-More Micro, and 2 GS3 drives using the MODBUS RTU protocol. It appears the C-More Micro has to be the master on the network, but I believe I need the PLC to be the master of the network so I can send and receive from the GS3's. I wish to do this so I can have the network up and running, the machine operational, and be able to go online with the PLC for troubleshooting. Any previous experiences or help would be appreciated. WJones


  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2014

    Created by: Steve Bailey

    There can only be one master on a Modbus RTU network.

    Consider setting up two networks. One with the DL06 and the drives where the DLO6 is the master. The second with the DL06 and the C-More Micro with the C-More Micro as master. I have done that with a DL06, a 6 " C-More, and a SureServo drive.

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2014

    Created by: wjones

    If you do set up 2 networks, can you still be online with the PLC while things are connected and running?

    Thanks,

    Walt Jones

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2014

    Created by: Steve Bailey

    If you have a spare slot in the DL06 you could install an ECOM module in it. Otherwise you will have to disconnect one of the serial ports to go online with DirectSoft.

  • adccommunitymod (AutomationDirect)

    Created Date: March 09,2014

    Created by: wjones

    I would like to set up a 485 network to communicate with a DL006 (secondary port), a C-More Micro, and 2 GS3 drives using the MODBUS RTU protocol. It appears the C-More Micro has to be the master on the network, but I believe I need the PLC to be the master of the network so I can send and receive from the GS3's. I wish to do this so I can have the network up and running, the machine operational, and be able to go online with the PLC for troubleshooting. Any previous experiences or help would be appreciated.

    WJones