Click's + DL06 for House automation

Created Date: January 16,2013

Created By: Rastislav

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello, I'm seriously considering using Click or more than 1 Click with DL06 for home automation purposes. My idea is to use Click for digital in/out (Alarm, Lights) connected to DL06 via modbus/RTU. DL06 ,since it already has analog inputs, will take care of heat pump and air ventilation together with CO2/humidity/pollen sensors on modbus/RTU (using another rs485 bus). This way, only programming interface to setup everything (except modbus communication on Click - 1 rung with END ) will be DirectLogic05 and this modularity will allow having 1 Click/floor with I/O modules required by that floor. Question is about topology. Is it possible to use 1 or more Click with modules as Modbus Slave's to DL06 and control outputs on Click,using Click inputs by DL06? (I apologize if question is too dumb, I haven't read all documentation yet) Is there any documentation showing possible scenarios?


  • adccommunitymod (AutomationDirect)

    Created Date: January 16,2013

    Created by: Mike@Forshock

    The 06 controller can talk to multiple units just fine, including Click.

    Since you appear to be running all the lines to a main area, why not just use the 06 itself for everything? Running the serial cable, you may as well just run the digitals directly.

  • adccommunitymod (AutomationDirect)

    Created Date: January 17,2013

    Created by: Rastislav

    No, lines will be running to 1 area/floor. With 3 floors there will be 2x Click's and 1x DL06.

    DL06 does not have number of I/O required, since I'm going to use about half CPU I/O of DL06 for heat pump and ventilation. Reason for using Click for digital I/O is price. Also having Click on each floor simplifies cabling and allows for expansion.

    By connecting Click and DL06 using RS485 modbus (I plan to attach more devices such as 1-wire to modbus adapter, HMI, RFID) my only expandability option will be extending RS485 cable or getting DL06 communication module.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 17,2013

    Created by: Mike@Forshock

    Using the RS485 and Modbus RTU you will have access to the CLICK from an 06

    In the CLICK "Address Picker " you will see the registers (DF1, DS1, etc.), turn on "Display Modbus address " and choose HEX. This will give the addresses need to enter on the 06 to pull the data from the CLICK.

    CO2, Pollen and Humidity... Interesting mix.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 16,2013

    Created by: Rastislav

    Hello,

    I'm seriously considering using Click or more than 1 Click with DL06 for home automation purposes.

    My idea is to use Click for digital in/out (Alarm, Lights) connected to DL06 via modbus/RTU.

    DL06 ,since it already has analog inputs, will take care of heat pump and air ventilation together with CO2/humidity/pollen sensors on modbus/RTU (using another rs485 bus).

    This way, only programming interface to setup everything (except modbus communication on Click - 1 rung with END ) will be DirectLogic05 and this modularity will allow having 1 Click/floor with I/O modules required by that floor.

    Question is about topology.

    Is it possible to use 1 or more Click with modules as Modbus Slave's to DL06 and control outputs on Click,using Click inputs by DL06? (I apologize if question is too dumb, I haven't read all documentation yet)

    Is there any documentation showing possible scenarios?

    Expand Post