Hi all What does it mean when all the LEDs continue to flash on and off for about 60 seconds and then go off. I have removed all the modules and applied power the Power and CPU leds flash for about 60 seconds and then go out. PLC = DL405


  • adccommunitymod (AutomationDirect)

    Created Date: August 27,2012

    Created by: Do-more PE

    This typically indicates that the PLC power is incorrect or that the PLC power supply itself is damaged.

    Check the incoming power with a multimeter. Also check to be sure that the power selection jumper is in the correct position. If this checks out, remove the PLC CPU/Power Supply from the base and power it by itself. If the condition persists, replace the PLC CPU/Power Supply.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 28,2012

    Created by: timk

    Thats what I was afraid of.

    Thanks

  • adccommunitymod (AutomationDirect)

    Created Date: August 27,2012

    Created by: timk