Dl05 up down counter

Created Date: August 04,2011

Created By: bilt2spd

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Is there a way to limit the UP count on an UP DOWN COUNTER? I want to be able to count from 0 to 3 and not go past if the UP input is fed again. Any help is appreciated.


  • adccommunitymod (AutomationDirect)

    Created Date: August 05,2011

    Created by: milldrone

    bilt2spd,

    Give this a try. Copy the text below, save in notepad, start a new instance of Direct Soft 5. Click on file, import, program, find the notepad file you just saved, click on open. Direct Soft 5 will do the rest.

    PLC 05

    // Rung 1

    // Address 0

    #BEGIN COMMENT

    "http://forum.automationdirect.com/showthread.php?t=8497 "

    " "

    "Is there a way to limit the UP count on an UP DOWN COUNTER? I want to be able to "

    "count from 0 to 3 and not go past if the UP input is fed again. Any help is appreciated. "

    #END

    STR X0

    ANDN CTA0 K3

    STR X1

    STR X3

    UDC CT0 K0

    // Rung 2

    // Address 8

    END

    // Rung 3

    // Address 9

    NOP

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: September 02,2011

    Created by: tommycai

    have you tried counter example on 5-47 of the dl205 usermanual and have that bit after three reset the up down counter?

  • adccommunitymod (AutomationDirect)

    Created Date: August 04,2011

    Created by: bilt2spd

    Is there a way to limit the UP count on an UP DOWN COUNTER? I want to be able to count from 0 to 3 and not go past if the UP input is fed again. Any help is appreciated.