adccommunitymod (AutomationDirect) asked a question.

adding an output module

Created Date: July 18,2011

Created By: RonR399

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a 4 output cpu & I added a 16 output module. How do I get Y001 to work on the 16 output module? I have Y005 operating in the software but Y001 on the 16 output module does not operate. what do I need to do? all my modules show in the i/o config.


  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: Gvanauken

    Which PLC are you using?

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: RonR399

    C0-02DR-D PLC

    & a C0-16TD2 Module

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: bcarlton

    In the Click software go to 'setup '. Choose 'system Configuration '. Add in your power supply, the CPU and the add-on module. Note the assignment of the outputs. There is no Y5.

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: RonR399

    no Y5 in the cpu, that is correct. my config shows all the modules.

    so, which "Y " is input 1 on the 16 input module?

    so, which "X " is output 1 on the 16 output module?

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: bcarlton

    Did you do the configuration I detailed? Did you LOOK at the table?

    There is NO Y5 Anywhere.

    The CPU has inputs X1 through X4. It has outputs Y1 through Y4

    The add on module has only outputs starting at Y101.

    Please read carefully.

    Inputs are 'X ', outputs are 'Y '.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: RonR399

    oh, ok. i get it now.

    thanks

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: RonR399

    I changed it to Y101 but it still does not energize the relay, it does energize the relay in the software

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: bcarlton

    I can't test this on my end. I have a Click but no add on module. Sorry.

    Are you saying that the top light on the add on module does not light up? Or that something you attached to the terminal does not turn on?

  • adccommunitymod (AutomationDirect)

    Created Date: July 18,2011

    Created by: RonR399

    no light on the module output indicator, the software shows the output working.

  • adccommunitymod (AutomationDirect)

    Created Date: July 19,2011

    Created by: bcarlton

    If you wish, go to where the Click project file is stored. Possibly 'my Documents ' - 'Automation Direct ' - 'Click '- 'Project '. Right click on it and choose 'send To Compressed Folder '. This will create a 'zip ' file with the same name.

    Then start a post here. Scroll down to 'manage Attachments '. Hit the browse button to search through your own computer to find the zip file. Press 'Upload ' to send it to this site. The 'submit ' your post. The file will be attached and we can check it and maybe help you further.

    If you would rather I think you can attach it to a Private message.