I have a f0-04ad-1 I am playing around with. I am feeding it a 4-20 signal from my flue process meter, and have all the inputs set right. I am trying to simulate a 0-150 psi pressure transducer I plan on adding to our application. The problem I am having is that the resolution after I do the scaling is in whole decimals, and I would much rather have it a little more precise, say down to 1/10's of a PSI, which should be no problem. I am using a ibox to load the values into v401,v402,v403, and v404. on the next rung, I have LD(401) ---- > MUL(k150) ---- > DIV(k4095) ----- >OUT(V2010). The math works fine, but stores the number as a whole digit, and not a real. Any thoughts?? Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: April 14,2011

    Created by: franji1

    try this

    LD V401

    MUL K150

    BIN // CONVERT BCD VALUE TO BINARY

    BTOR // CONVERT BINARY TO REAL

    DIVR R4095.0 // DIVIDE BY 4095.0 REAL

    OUTD V2010 // OUTPUT TO 32BIT V2010-V2011

    now look at V2010 in Data View as a REAL and you should be getting what you want

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 14,2011

    Created by: bfitz

    Alternately, if you didn't want to use reals in your program (inline compares are gone), you could just change your MUL(k150) to MUL(k1500) to imply a decimal point. You will need to alter all your setpoints or alarm values etc. to match the implied decimal place, but most HMIs can be setup to do this transparently.

    Brian

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 14,2011

    Created by: joe_haase

    try this

    LD V401

    MUL K150

    BIN // CONVERT BCD VALUE TO BINARY

    BTOR // CONVERT BINARY TO REAL

    DIVR R4095.0 // DIVIDE BY 4095.0 REAL

    OUTD V2010 // OUTPUT TO 32BIT V2010-V2011

    now look at V2010 in Data View as a REAL and you should be getting what you want

    When I scale my output to 20mA, simulating a output of 150psi, I get a v2010 of 0.9995116..... 12mA gives me 0.4999

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 14,2011

    Created by: joe_haase

    Alternately, if you didn't want to use reals in your program (inline compares are gone), you could just change your MUL(k150) to MUL(k1500) to imply a decimal point. You will need to alter all your setpoints or alarm values etc. to match the implied decimal place, but most HMIs can be setup to do this transparently.

    Brian

    by changing to k1500... I see how I'm getting the extra decimal that I wanted. Now my next task is to convert over to a decimal from a BCD number.

    My mind has been shot as they switched me to third shift this week, and I ', playing catch up/

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 18,2011

    Created by: Bob S BN

    by changing to k1500... I see how I'm getting the extra decimal that I wanted. Now my next task is to convert over to a decimal from a BCD number.

    What do you need the "decimal " for??

    What Brian was hinting at is many HMI's, including the CMORE line can be set up to display a BCD number with the decimal point where you want it. While the decimal is "implied " in the PLC logic, the HMI numeric displays and numeric entry can have the decimal point showing to the operator just like it belongs there.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 21,2011

    Created by: robertkeenan

    Working With Binary Data

    I am trying to do something similar with a F4-04AD-1 and I notice that you do a BIN conversion with the data from the sensor. If I load the data as binary

    LD K8200 (8 means read as binary)

    OUT V710 (Slot 2 on DL06)

    this will do away with the need for conversion, but when I go to do my scaling will I be doing it the same way.

    LD V401

    MUL K150

    BTOR // CONVERT BINARY TO REAL

    DIVR R4095.0 // DIVIDE BY 4095.0 REAL

    OUTD V2010 // OUTPUT TO 32BIT V2010-V2011

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 21,2011

    Created by: joe_haase

    What do you need the "decimal " for??

    What Brian was hinting at is many HMI's, including the CMORE line can be set up to display a BCD number with the decimal point where you want it. While the decimal is "implied " in the PLC logic, the HMI numeric displays and numeric entry can have the decimal point showing to the operator just like it belongs there.

    I will be trying HMIMax with this setup. When I do the basic conversion using the built in scaling iBox, it only loads a whole number into the memory address. Since the card and the sensor can handle better resolution, I wanted to take advantage of it. I reworked the math and got my PT100 to show in the 100's of a degree, a big advancment over getting "68 " degrees as a output.

    I am trying to do something similar with a F4-04AD-1 and I notice that you do a BIN conversion with the data from the sensor. If I load the data as binary

    LD K8200 (8 means read as binary)

    OUT V710 (Slot 2 on DL06)

    this will do away with the need for conversion, but when I go to do my scaling will I be doing it the same way.

    LD V401

    MUL K150

    BTOR // CONVERT BINARY TO REAL

    DIVR R4095.0 // DIVIDE BY 4095.0 REAL

    OUTD V2010 // OUTPUT TO 32BIT V2010-V2011

    Why not just use the iBox to load the values into the DL06 as BCD, then do basic math with the BCD number instead of converting to real? I couldn't get the output correct by going with a real#.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 13,2011

    Created by: joe_haase

    I have a f0-04ad-1 I am playing around with. I am feeding it a 4-20 signal from my flue process meter, and have all the inputs set right.

    I am trying to simulate a 0-150 psi pressure transducer I plan on adding to our application.

    The problem I am having is that the resolution after I do the scaling is in whole decimals, and I would much rather have it a little more precise, say down to 1/10's of a PSI, which should be no problem.

    I am using a ibox to load the values into v401,v402,v403, and v404.

    on the next rung, I have LD(401) ----> MUL(k150) ----> DIV(k4095) ----->OUT(V2010).

    The math works fine, but stores the number as a whole digit, and not a real.

    Any thoughts?? Thanks

    Expand Post