SLC 500 conversion
Created Date: October 25,2010
Created By: tmoney
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I am converting a SLC 500 to a DL06. I have figured everything out except one bit. In my SLC program their is a bit B3/15, this bit has no output. I am hoping that someone might know what this bit is intended for.
Created Date: October 25,2010
Created by: bcarlton
It may have ben set/reset by an HMI-display connection.
Created Date: October 25,2010
Created by: tmoney
I do not have a HMI, and this bit is relevant to the machine operation. I noticed both NC and NO of this bit are in a rung with a counter in them.
Created Date: October 25,2010
Created by: Steve Bailey
A normally open and normally closed contact in series creates a "Never True " condition. A normally open and normally closed contact in parallel creates an "Always True " condition. No coil instruction required.
Created Date: October 26,2010
Created by: Shimmy
In which case you can replace the NO and NC b3/15 bit with either sp1 (always true) or sp2 (never true).
Created Date: October 25,2010
Created by: tmoney
I am converting a SLC 500 to a DL06. I have figured everything out except one bit. In my SLC program their is a bit B3/15, this bit has no output. I am hoping that someone might know what this bit is intended for.