Hi Everybody Can anybody point me in the right direction on how to network 2 Dl06 plcs together with ethernet modules. the plcs need to be able to toggle each others inputs and outputs. Is this even possible and if so what instructions would i be using. I will also have a c-more touch screen also on the same panel reading and writing to both plcs. any help would be appreciated.


  • adccommunitymod (AutomationDirect)

    Created Date: August 04,2010

    Created by: bcarlton

    The PLCs would not DIRECTLY control the inputs and outputs of the other. Each PLC should write to a group of 'C ' bits in the other. This would be the fastest. Each PLC would then evaluate its own inputs, the 'C ' bits from the other PLC and other appropriate logic to turn on its own outputs.

  • adccommunitymod (AutomationDirect)

    Created Date: August 04,2010

    Created by: JoeW

    Heres my quick rundown:

    -Connect to the ECOM100 using NetEdit 3 and setup your IP addresses, Subnet and Module ID.

    -In your PLC program use the ECOM100 IBox to "tell " the PLC that it has an ECOM100 installed.

    -Use ECWX to write data to the other PLC or ECRX to read data from the other PLC.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 04,2010

    Created by: rilver

    Hi Everybody

    Can anybody point me in the right direction on how to network 2 Dl06 plcs together with ethernet modules. the plcs need to be able to toggle each others inputs and outputs. Is this even possible and if so what instructions would i be using. I will also have a c-more touch screen also on the same panel reading and writing to both plcs. any help would be appreciated.

    Expand Post