CTRIO H2 for use with quad encoder

Created Date: June 18,2010

Created By: eric14779

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am spec-ing out a linear encoder for use with a CTRIO H2 counter I know what mechanical resolution I want. but I am confused as to what the minimum edge separation can be to work with the CTRIO H2 counter The output of the encoder is Quadrature in a range of 0.12 microsecond to 24.0 microsecond edge separation the encoder is a Balluff BML-S1B0-Q53F-M400 and insight would be appreciated


  • adccommunitymod (AutomationDirect)

    Created Date: June 18,2010

    Created by: Rich19551

    Minimum Pulse Width 5 ?sec

    1 Millisecond = 1000 Micro seconds

  • adccommunitymod (AutomationDirect)

    Created Date: June 19,2010

    Created by: eric14779

    Thanks for the reply Rich19551

    would the CTRIO H2 handle a 5 ?sec pulse on each input or would I have to multipy by 4 to not have too high of a freq.

    in other words what is the fastest quadrature signal the H2 can handle ???

  • adccommunitymod (AutomationDirect)

    Created Date: June 19,2010

    Created by: Rich19551

    2 quadrature encoder counters up to 100kHz, or 1us

    The H2 is desined to run independent of the CPU to drive it's own I/O but if you are trying to use the information in the CPU you are limited to scan time.

    Be carefull of what you are trying to do.

    Rich

  • adccommunitymod (AutomationDirect)

    Created Date: June 21,2010

    Created by: eric14779

    Rich,

    I am designing a system simular to a DRO with the ability to calculate a "distance to position " read out on a C-More display panel.

    this device will be hand cranked like a manual lathe into position. As the operator gets close he will move the slide slower so my thinking was that the scan time issue will not be a factor.

    The PLC will not have any other "duties " other than calculating the math for the recipie part selected, 1 output inhibit when the slide is between two positions, and calculating the value to display.

    so I think the scan time will be very short....

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 18,2010

    Created by: eric14779

    I am spec-ing out a linear encoder for use with a CTRIO H2 counter I know what mechanical resolution I want.

    but I am confused as to what the minimum edge separation can be to work with the CTRIO H2 counter

    The output of the encoder is Quadrature in a range of 0.12 microsecond to 24.0 microsecond edge separation

    the encoder is a Balluff BML-S1B0-Q53F-M400

    and insight would be appreciated

    Expand Post