I have set up the 05 for high speed counter operation and configured it for external reset with interrupt using X2. This works perfectly and the counter resets on the leading edge and continues counting immediately as desired. My problem is that the counter resets agin on the trailing edge. Is there any way of preventing this? :(


  • adccommunitymod (AutomationDirect)

    Created Date: September 11,2009

    Created by: bcarlton

    It's possible that your triggering device is bouncing. Is it a hard contact switch of some type?

  • adccommunitymod (AutomationDirect)

    Created Date: March 09,2010

    Created by: klindner

    I also have a reset question along this line.

    I'm also using an 05 in a high speed counter operation but I would like to

    reset the counter internally after my CMPD has reached my preset value.

    Everything works great when I reset the counter using an external input

    like a prox switch. Does anyone have any suggestions how to reset my

    counter internally after my CMPD has reached its preset value?

    Your help is greatly appreciated.

    Thanks

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 09,2010

    Created by: bcarlton

    You are using UDC CT76 as the high speed counter. The third leg is the Reset input. Simply make that legs contact TRUE to reset the counter.

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2010

    Created by: klindner

    05 Counter reset

    Thanks for the reply,

    I 've tried a few different ways to reset the contact placed on that rung.

    I'm using two CMPD boxes after the counter. I can successfully generate

    individual outputs from each CMPD as they reach their individual preset.

    After the second CMPD I would like to reset the counter which is driven by

    an encoder. It appears I need to use input X2 on my PLC as the reset contact

    and input. Is there a virtual way to turn on this contact without using an

    actual external input such as a prox switch? I would like to reset the counter

    after the second CMPD box has reached its ' preset.

    Thanks for your help

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2010

    Created by: klindner

    Counter reset solved

    Hello,

    I was able to use a control relay to reset the counter.

    I'm a plc novice and fortunately there's an online

    manual to study.

    Thanks

  • adccommunitymod (AutomationDirect)

    Created Date: March 10,2010

    Created by: bcarlton

    You would use the external contact when there is a detectable event (the switch being hit by something for example) where you want to reset the count. The setup of the counter function allows you to choose if you wish to use X2, with or without an interrupt, as a reset.

    If you don't have any external event as a reference then just set that to 'filtered input '. Place a control relay contact (which is driven by the result of your compare) in that third leg instead of (or in parallel to) whatever else you have there.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: September 11,2009

    Created by: Jay Smit

    I have set up the 05 for high speed counter operation and configured it for external reset with interrupt using X2. This works perfectly and the counter resets on the leading edge and continues counting immediately as desired.

    My problem is that the counter resets agin on the trailing edge. Is there any way of preventing this? :(