adccommunitymod (AutomationDirect) asked a question.
Divide RTD Temp Reading
Created Date: January 16,2009
Created By: twitte
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have a fairly basic question which I can't solve. How can I divide my RTD card reading (F2-04RTD) by 10 so I can properly display it on my HMI. I tried using LD (vmemory of reading) DIV (k10) and OUT (new v memory), but this did not work. Any help would be great. Thank You Tyson
Created Date: January 17,2009
Created by: KPrice
twitte, A couple of questions come to mind,
Did you setup the data format for binary or BCD?
You may need to use double-word instructions with BCD format.
The DIV instruction is a single-word BCD instruction.
Is your temperature value negative?
Could you be over-writing the V-memory location that holds your calculated temperature?
Have you tried the SHFR K4 instruction to remove first digit?
Your HMI may have a scaling feature available with your numeric display object.
Do any of these ideas this help?
Created Date: January 19,2009
Created by: twitte
Thanks for the suggestions.
Right now I have it set up for binary numbers, I will try changing it to BCD. I will also try removing the first digit with the command you listed. When I tried dividing before I was using a new v memory location. All my reading are unipolar. I realized you can scale on the HMI for some situations, but not for all situations, like the graph feature on the CMORE.
Thank You
Created Date: January 19,2009
Created by: a agnone
Yes, do it in BCD. I just used the ladder from the book and then used a Display Numeric in the C-More. Works just fine.
Created Date: January 21,2009
Created by: JimHoward
twitte,
Following is my method of working with the F2-04RTD module. Display the result V2010 on your HMI as real, as it will show both positive and negative temperatures.
PLC 260
// Rung 1
// Address 0
#BEGIN COMMENT
"First, the raw RTD data is 15 bit Binary, with a " "sign bit " ", in the format " "magnitude plus "
"sign " ". The sign bit is masked off with the ANDD function, before the Binary data word is "
"converted to Real. As the data is in tenths of degrees, divide by 10 for whole degrees. "
#END
STR SP1
LD V2000
ANDD K7fff
BTOR
DIVR R10
// Rung 2
// Address 8
#BEGIN COMMENT
"Second, if the sign bit is ON (which indicates a temperature below zero), multiply the "
"above real temperature data by -1 to make the real temperature data negative. "
#END
STR B2000.15
MULR R-1
// Rung 3
// Address 13
#BEGIN COMMENT
"Third, filter and smooth the real temperature data, which helps reject any noise induced "
"into the field wiring. The filter simply takes the difference between the previous filtered "
"data (scratchpad) and the current data, and multiplies it (MULR) by a " "filter factor " " (note, "
"a smaller number increases the filtering) and adds/subtracts that to/from the previous "
"filtered data. "
#END
STR SP1
SUBR V2020
MULR R0.2
ADDR V2020
OUTD V2020
OUTD V2010
// Rung 4
// Address 21
STRN SP0
AND X50
OUT C1000
// Rung 5
// Address 24
NOP
#BEGIN ELEMENT_DOC
"X50 ", "XMTR_RTD-1 ", " ", "Broken XMTR, RTD Input - Base0/Slot2/Ch1 "
"C1000 ", "XMTRRTD1 ", " ", "Broken XMTR, RTD Input - Base0/Slot2/Ch1 "
"V2000 ", "_RTD-1 ", " ", "Raw RTD Input - Base0/Slot2/Ch1 (Binary) "
"V2010 ", "RTD1 ", " ", "Air Inlet Temperature (Filtered, Real) "
"V2020 ", "__RTD-1 ", " ", "Scratchpad RTD Input - Base0/Slot2/Ch1 (Real) "
"B2000.15 ", "Sign_RTD-1 ", " ", "Sign Bit, Raw RTD Input - Base0/Slot2/Ch1 "
#END
Created Date: January 16,2009
Created by: twitte
I have a fairly basic question which I can't solve. How can I divide my RTD card reading (F2-04RTD) by 10 so I can properly display it on my HMI. I tried using LD (vmemory of reading) DIV (k10) and OUT (new v memory), but this did not work. Any help would be great.
Thank You
Tyson