adccommunitymod (AutomationDirect) asked a question.

Bad D2-EM

Created Date: December 29,2007

Created By: tmuld24

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have just installed 2 9 slot -1 bases, with the D2-CM and 2 x D2-EM. 260 CPU comes on and works, CM lights up, but no lights or functional comms thru the 2 - D2-EM's. Both bad out of the box??


  • adccommunitymod (AutomationDirect)

    Created Date: December 31,2007

    Created by: a agnone

    Check to make sure the units are properly seated to the bases. I noticed when I installed mine, it was hard to align the pins, I had to install them couple times. The one did not "feel right " when I tried to tightned the screws to the side of the base.

  • adccommunitymod (AutomationDirect)

    Created Date: January 02,2008

    Created by: stimpsonjcat

    CM module is set to 1?

    Both EM modules set to ON for term?

    Do you see the expansion base at all under PLC/Config IO?

  • adccommunitymod (AutomationDirect)

    Created Date: January 15,2008

    Created by: tmuld24

    NO, the PLC will not recognize the expansion at all.

    Trying to ensure all of the connectors are seated, they look fine.

    Still not lights, tried CM on all 4 settings, and both switches are up.

    Now what, this is VERY frustrating!

  • adccommunitymod (AutomationDirect)

    Created Date: January 15,2008

    Created by: FACTSTech

    Where did you get the cables connecting the EM modules? Are they pinned 1-1,2-2 and so on? If not they are the wrong cables.

  • adccommunitymod (AutomationDirect)

    Created Date: December 29,2007

    Created by: tmuld24

    I have just installed 2 9 slot -1 bases, with the D2-CM and 2 x D2-EM.

    260 CPU comes on and works, CM lights up, but no lights or functional comms thru the 2 - D2-EM's.

    Both bad out of the box??