I am looking to scale an analog output for an electo-pneumatic transducer. I want to have an HMI input determine what pressure to run the process. I'm using a DL-06. Any suggestions?


  • adccommunitymod (AutomationDirect)

    Created Date: October 18,2007

    Created by: KPrice

    roboteacher, I'll make some assumptions,

    12-bit (0-4095 BCD) analog output

    HMI adjusts output in V-2000 (0-100 BCD no decimal point)

    Output V-memory V3000 (set by analog config)

    Then your scaling would be:

    LD V2000 (0-100 BCD)

    MUL K4095 (analog output full scale)

    DIV K100 (adjustment full scale)

    OUT V3000 (analog output register)

    Is this what you 're looking for?

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 18,2007

    Created by: KPrice

    roboteacher, after posting, it dawned on me that you may be looking for suggestions for hardware? I suggest the C-more for your operator interface. Look at the following link for I/Ps.

    http://www.davis.com/Default.aspx?page=category%20search%20results&CatList=1015&Parent=989&tree=852*Pressure+Measurement*0@@957*Pressure+Transmitters*0@@989*I-P+(Current+to+Pressur e)+-+E-P+(Voltage+to+Pressure)+Transducers*1015@@

    Hope this helps

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 18,2007

    Created by: roboteacher

    I am looking to scale an analog output for an electo-pneumatic transducer. I want to have an HMI input determine what pressure to run the process. I'm using a DL-06.

    Any suggestions?