adccommunitymod (AutomationDirect) asked a question.

Reading Scale Weight with DL06

Created Date: October 09,2007

Created By: SoundBiodiesel.com

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Manual says have to use to line of ladder in RS232 sending device. How do you read the weight from a device you can't enter lines of ladder


  • adccommunitymod (AutomationDirect)

    Created Date: October 09,2007

    Created by: SoundBiodiesel.com

    Manual says have to use two lines of ladder in the RS232 connected sending device. How do you read the weight from a device you can't enter lines of ladder into.

  • adccommunitymod (AutomationDirect)

    Created Date: October 09,2007

    Created by: jackson

    That's not what the manual is saying. You need to write ladder code in the PLC to receive ASCII data.

    Look at chapter 5 at the instructions. Look specifically for the AIN (ASCII IN) instruction.

  • adccommunitymod (AutomationDirect)

    Created Date: October 09,2007

    Created by: SoundBiodiesel.com

    Thanks I was looking in the D0-DCM manual. Chap 5 of the PLC has the info I needed ! !