Extended Timer

Created Date: June 22,2007

Created By: jamesjcooper

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello all, the amount of information on this forum is rather amazing. I just started playing with PLC's about six hours ago and learned ladder logic from various posts here, thank you all for the crash course. My question is how can I have a long timer, I want to fire a timer and have it hold an output on for 30 minutes and another for an hour. My application is in a vehicle and I want to be able to leave my inverter on for a period of time after I get out to finish charging batteries, or whatever else I have plugged in. I have gotten it to work with two shorter timers controlling the same output but just need to extend the time. 999.9 Seconds only gives me 16 minutes. Can I just daisy chain timers together? Basically have four 15 minute timers which when one ends starts the next? My hardware is a DL05 with a C-more non-touch panel. Using S bits for the control between the panel and the PLC. I appreciate any help and thank you in advance. Jim Cooper


  • adccommunitymod (AutomationDirect)

    Created Date: June 22,2007

    Created by: sii

    Check out the TMRA instruction. It lets you go up to 9999999.9 in increments of 1/10 second. It is a two input timer as opposed to a 1 input (TMR). The following should give you what you want, X0 being the trigger to start the timer, Y0 the output you wish to stay on. The "K50 " in rung 2 gives a 5 second timer, just change the 50 to whatever time you desire.

    // Rung 1

    // Address 0

    STRPD X0

    STR C0

    ANDN T0

    ORSTR

    OUT C0

    // Rung 2

    // Address 5

    STR C0

    STR T0

    TMRA T0 K50

    // Rung 3

    // Address 10

    STR C0

    OUT Y0

    // Rung 4

    // Address 12

    END

    // Rung 5

    // Address 13

    NOP

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 22,2007

    Created by: jamesjcooper

    Thank you for the help, I will try it when I get home.

    I just want to make sure I am reading this right, that I will use TMRA but with only one trigger? I am just trying to visualize this as ladder rungs.

  • adccommunitymod (AutomationDirect)

    Created Date: June 23,2007

    Created by: jamesjcooper

    Ok, I got the TMRA working, I assume the top line is the trigger and the bottom in the reset?

    My only problem remaining is that every time I reload the program, or cycle power to the CPU, all the timers activate, one of which is 3 hours. Is there any way to prevent this? In four words of ladder or less? (I am at 96 words and only have the free version)

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 23,2007

    Created by: sii

    Do you know how to post your ladder logic here?

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: jamesjcooper

    Like this?

    PLC 05

    // Rung 1

    // Address 0

    STR X5

    SET S16 S16

    // Rung 2

    // Address 3

    STR S1

    OR S6

    STRN X0

    OR S16

    ANDSTR

    OUT Y1

    // Rung 3

    // Address 9

    STR S2

    OR S6

    STRN X0

    OR S16

    ANDSTR

    OUT Y2

    // Rung 4

    // Address 15

    STR S3

    OR S6

    STRN X0

    OR S16

    ANDSTR

    OUT Y3

    // Rung 5

    // Address 21

    STRN S12

    STR S12

    TMRA T4 K3600000

    // Rung 6

    // Address 26

    STRN S13

    STR S13

    TMRA T6 K10800000

    // Rung 7

    // Address 31

    STR S4

    STRN T4

    ORN T6

    AND S21

    ORSTR

    OUT Y4

    // Rung 8

    // Address 37

    STRN S15

    TMR T3 K6000

    // Rung 9

    // Address 41

    STR S5

    STRN X0

    OR X5

    OR S16

    ANDSTR

    STRN T3

    AND S20

    ORSTR

    OR S15

    OR X4

    OUT Y5

    // Rung 10

    // Address 52

    STRN S7

    STR S7

    TMRA T10 K1800000

    // Rung 11

    // Address 57

    STRN S10

    STR S7

    TMRA T12 K3600000

    // Rung 12

    // Address 62

    STRN T12

    ORN T10

    AND S20

    STR S0

    STRN X0

    OR X5

    OR S16

    ANDSTR

    ORSTR

    ANDN X2

    OUT Y0

    // Rung 13

    // Address 73

    STR Y1

    OR Y2

    OR Y3

    SET S11 S11

    // Rung 14

    // Address 78

    STRN Y1

    ANDN Y2

    ANDN Y3

    RST S11 S11

    // Rung 15

    // Address 83

    STR X1

    LD K5

    OUT V3000

    // Rung 16

    // Address 86

    STRN X1

    LD K999

    OUT V3000

    // Rung 17

    // Address 89

    STR X1

    LD K5

    OUT V3002

    // Rung 18

    // Address 92

    STRN X1

    LD K0

    OUT V3002

    // Rung 19

    // Address 95

    END

    // Rung 20

    // Address 96

    NOP

    #BEGIN ELEMENT_DOC

    "UB ", "T8 ", " ", " "

    "X0 ", "Acc Power ", " ", " "

    "X1 ", "Inverter Fault ", " ", " "

    "X2 ", "Inverter Low Vol ", " ", " "

    "X3 ", "Inverter Ok ", " ", " "

    "X4 ", "Cargo Lights Inp ", " ", " "

    "X5 ", "Acc Over Sw ", " ", " "

    "Y0 ", "Inverter Relay ", " ", " "

    "Y1 ", "H/L Strobe Relay ", " ", " "

    "Y2 ", "Dash Light Relay ", " ", " "

    "Y3 ", "T/L Strobe Relay ", " ", " "

    "Y4 ", "Radio Relay ", " ", " "

    "Y5 ", "Cargo Lght Relay ", " ", " "

    "S0 ", "Inverter On ", " ", " "

    "S1 ", "H/L Strobe ", " ", " "

    "S2 ", "Dash Light ", " ", " "

    "S3 ", "T/L Strobe ", " ", " "

    "S4 ", "Radio ", " ", " "

    "S5 ", "Cargo Light ", " ", " "

    "S6 ", "All Warning ", " ", " "

    "S7 ", "Inverter 30 min ", " ", " "

    "S10 ", "Inverter 1 Hour ", " ", " "

    "S11 ", "Warning On ", " ", " "

    "S12 ", "Radio 1 Hour ", " ", " "

    "S13 ", "Radio 3 Hours ", " ", " "

    "S15 ", "Cargo 10 Minutes ", " ", " "

    "S16 ", "Acc Override ", " ", " "

    "S20 ", "Timer Enable ", " ", " "

    "S21 ", "Radio Tmr Enable ", " ", " "

    "T3 ", "Cargo 10 Min Tmr ", " ", " "

    "T4 ", "Radio 1 Hour Tmr ", " ", " "

    "T6 ", "Radio 3 Hour Tmr ", " ", " "

    "T10 ", "Invrt 30 Min Tmr ", " ", " "

    "T12 ", "Invrt 1 Hr Tmr ", " ", " "

    #END

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 25,2007

    Created by: milldrone

    jamesjcooper,

    I don't think it will make any difference in program size but we normally use "C " bits for internal relays and "S " bits for stages. I only say this because I don't see any stages.

    On rung #5 you are using S12/ to start your timer. I cannot find any coil or bit setting logic to change it's state. When the PLC is first powered up any non retentive bits are cleared or off. So this bit would be off and your timer would start timing. Rung #6 has the same type of problems as rung #5. Rung #8 has the same type of problems as rung #5. Rung #10 has the same type of problems as rung #5. Rung #11 has the same type of problems as rung #5.

    After further cogitating on this, one posiblity I didn't think about earlier would be this:. You are using this Plc as a slave or a master, and the bits ( "S ") are being changed in another plc. If this is true we also need this information.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 25,2007

    Created by: jamesjcooper

    Sorry if some things are not clear, I forgot I have the hardware in front of me. The S bits are being set by the touch panel, they are tied to momentary buttons on the screen that I would use to start the timer.

    Thank you for the pointer on different memory bits, when I started this I wasn't sure what all the different memory types were, and I am still learning.

    I can make some changes and have these as 'c ' bits, would that help from the timers restarting or just make the code make more sense.

    I appreciate all your help.

    Jim

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 25,2007

    Created by: milldrone

    jamesjcooper ,

    For the sake of this conversation I'm going to presume (this always gets me introuble) that the "S " address numbers will stay the same but now have a "C " prefix now. So you have a panel some where that is setting bits for you. Have you confirmed the the bits are being set? I'm going to presume at this moment that they are. Do you have any handshaking in place so the plc knows what to do if the panel is not communicating? I can't see any so I'm presuming no. I'm also presuming that you have not altered the retentive ranges in the plc. "S21 " was the highest "S " bit you used previously so I'm going to suggest you use "C22 ". Then you would turn on "C22 " "always " with the HMI. Now for the bad news. when I series "C22 " with every timers ' count rung I get 101 words. how important is the timer accuracy can 1 minute increments work? Can 15 second increments work? I might be able to work something out.

    PS it looks like some of the logic in rung# 11 doesnt match up. You have your "inverter 30 min " resetting "inverter 1 hour "

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 25,2007

    Created by: milldrone

    jamesjcooper,

    I have rewritten your code. Exchanging the "S " bits for "C " bits and have made the word requirement (98). I think the reason your timers were counting up was that your hmi was not communicating at that time. I have also included "C22 " that you will have to configure in the HMI to always be on. As I mentioned before I'm presuming you have not modified the retentive ranges in the PLC. I'm curious about rungs 13 and 14. It seems to me that you would have access to Y1, Y2, Y3 in the HMI and you wouldn't need to set a bit (C11), and or reset it. This would give you a little more programming room if you needed more. BTW where I found some room was in your set/reset coils. If you only specify the first address slot it will still work. IE when you get the little window just type in the address once. If I were you I'd copy this into a new project so you don't loose anything.

    PLC 05

    // Rung 1

    // Address 0

    STR X5

    SET C16

    // Rung 2

    // Address 2

    STR C1

    OR C6

    STRN X0

    OR C16

    ANDSTR

    OUT Y1

    // Rung 3

    // Address 8

    STR C2

    OR C6

    STRN X0

    OR C16

    ANDSTR

    OUT Y2

    // Rung 4

    // Address 14

    STR C3

    OR C6

    STRN X0

    OR C16

    ANDSTR

    OUT Y3

    // Rung 5

    // Address 20

    STRN C12

    AND C22

    STR C12

    TMRA T4 K3600000

    // Rung 6

    // Address 26

    STRN C13

    AND C22

    STR C13

    TMRA T6 K10800000

    // Rung 7

    // Address 32

    STR C4

    STRN T4

    ORN T6

    AND C21

    ORSTR

    OUT Y4

    // Rung 8

    // Address 38

    STRN C15

    AND C22

    TMR T3 K6000

    // Rung 9

    // Address 43

    STR C5

    STRN X0

    OR X5

    OR C16

    ANDSTR

    STRN T3

    AND C20

    ORSTR

    OR C15

    OR X4

    OUT Y5

    // Rung 10

    // Address 54

    STRN C7

    AND C22

    STR C7

    TMRA T10 K1800000

    // Rung 11

    // Address 60

    STRN C10

    AND C22

    STR C10

    TMRA T12 K3600000

    // Rung 12

    // Address 66

    STRN T12

    ORN T10

    AND C20

    STR C0

    STRN X0

    OR X5

    OR C16

    ANDSTR

    ORSTR

    ANDN X2

    OUT Y0

    // Rung 13

    // Address 77

    STR Y1

    OR Y2

    OR Y3

    SET C11

    // Rung 14

    // Address 81

    STRN Y1

    ANDN Y2

    ANDN Y3

    RST C11

    // Rung 15

    // Address 85

    STR X1

    LD K5

    OUT V3000

    // Rung 16

    // Address 88

    STRN X1

    LD K999

    OUT V3000

    // Rung 17

    // Address 91

    STR X1

    LD K5

    OUT V3002

    // Rung 18

    // Address 94

    STRN X1

    LD K0

    OUT V3002

    // Rung 19

    // Address 97

    END

    // Rung 20

    // Address 98

    NOP

    #BEGIN ELEMENT_DOC

    "UB0 ", "T8 ", " ", " "

    "X0 ", "Acc Power ", " ", " "

    "X1 ", "Inverter Fault ", " ", " "

    "X2 ", "Inverter Low Vol ", " ", " "

    "X3 ", "Inverter Ok ", " ", " "

    "X4 ", "Cargo Lights Inp ", " ", " "

    "X5 ", "Acc Over Sw ", " ", " "

    "Y0 ", "Inverter Relay ", " ", " "

    "Y1 ", "H/L Strobe Relay ", " ", " "

    "Y2 ", "Dash Light Relay ", " ", " "

    "Y3 ", "T/L Strobe Relay ", " ", " "

    "Y4 ", "Radio Relay ", " ", " "

    "Y5 ", "Cargo Lght Relay ", " ", " "

    "C0 ", " ", " ", "inverter on "

    "C1 ", " ", " ", "h/l strobe "

    "C2 ", " ", " ", "dash light "

    "C3 ", " ", " ", "t/l strobe "

    "C4 ", " ", " ", "radio "

    "C5 ", " ", " ", "cargo light "

    "C6 ", " ", " ", "all warning "

    "C7 ", " ", " ", "inverter 30 min "

    "C10 ", " ", " ", "inverter 1 hour "

    "C11 ", " ", " ", "warning on "

    "C12 ", " ", " ", "radio 1 hour "

    "C13 ", " ", " ", "radio 3 hours "

    "C15 ", " ", " ", "cargo 15 minutes "

    "C16 ", " ", " ", "acc override "

    "C20 ", " ", " ", "timer enable "

    "C21 ", " ", " ", "radio timer enable "

    "C22 ", " ", " ", "always on from hmi "

    "S0 ", "Inverter On ", " ", " "

    "S1 ", "H/L Strobe ", " ", " "

    "S2 ", "Dash Light ", " ", " "

    "S3 ", "T/L Strobe ", " ", " "

    "S4 ", "Radio ", " ", " "

    "S5 ", "Cargo Light ", " ", " "

    "S6 ", "All Warning ", " ", " "

    "S7 ", "Inverter 30 min ", " ", " "

    "S10 ", "Inverter 1 Hour ", " ", " "

    "S11 ", "Warning On ", " ", " "

    "S12 ", "Radio 1 Hour ", " ", " "

    "S13 ", "Radio 3 Hours ", " ", " "

    "S15 ", "Cargo 10 Minutes ", " ", " "

    "S16 ", "Acc Override ", " ", " "

    "S20 ", "Timer Enable ", " ", " "

    "S21 ", "Radio Tmr Enable ", " ", " "

    "T3 ", "Cargo 10 Min Tmr ", " ", " "

    "T4 ", "Radio 1 Hour Tmr ", " ", " "

    "T6 ", "Radio 3 Hour Tmr ", " ", " "

    "T10 ", "Invrt 30 Min Tmr ", " ", " "

    "T12 ", "Invrt 1 Hr Tmr ", " ", " "

    #END

    Vaughn

    PS My bad, if I had read your first post more carefully I would have seen you were using a Cmore.

    Expand Post
10 of 24