adccommunitymod (AutomationDirect) asked a question.

Analog Output Not Functioning...

Created Date: June 17,2007

Created By: tom.fnp

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hi, i have a pid loop that is adjusting an analog output signal that drives a proportional pneumatic valve. Using PID view i get the process variable changing in the right Vmem locations. I have set the analog out card up (F0-4AD2DA-1) using the pointers method and it is installed in slot 3 of a DL06DD. When trying to measure the 4-20 mA signal i get nothing with a DMM. when i connect the proportinal valve up it also doesnt respond. For the first scan SP0 i have: LD K8081 - use only output 1, and no inputs OUT V720 - Use Slot 3 chanel 1 LD O3000 OUT V721 LD O301 OUT V722 and in the output part of the PID loop i have: LD V3005 - Control output of PID BCD OUT V2010 - output 0-4095 signal to analog card Does this seem correct? It all seems to be working correctly on the PIC View screen!


  • adccommunitymod (AutomationDirect)

    Created Date: June 18,2007

    Created by: FACTSTech

    Tom,

    There are several thing you have setup incorrectly, please give AutomationDirect tech support a call 1-800-633-0405

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: tom.fnp

    Hi, I cannot give you a call as i am in new zealand and the PH number wont work. Can you please let me know or point me in the wright direction as to where i have gone wrong please?

    I have realised that i had both the PID and Analog using V3000, i Have changed them and now have this setup:

    For the first scan SP0 i have:

    LD K8081 - use only output 1, and no inputs

    OUT V720 - Use Slot 3 chanel 1

    LD O4000

    OUT V721

    LD O4010

    OUT V722

    and in the output part of the PID loop i have:

    LD V3005 - Control output of PID

    BCD

    OUT V4010 - output 0-4095 signal to analog card

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 25,2007

    Created by: FACTSTech

    Tom,

    Technically you do not need the input setup LD K8081 only LD k81, OUT V720, LDA O4010, OUT V722.

    Are you using LDA O4000, LDA O4010 respectively?

    You do not need the BCD command, you have the data format in V4010 set for binary.

    What CPU Version of firmware? You might should upgrade if very old, current is 2.30. http://support.automationdirect.com/firmware/binaries.html

    To Upgrade you will also need the Koyo Tool. http://support.automationdirect.com/firmware/index.html

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: June 17,2007

    Created by: tom.fnp

    Hi, i have a pid loop that is adjusting an analog output signal that drives a proportional pneumatic valve. Using PID view i get the process variable changing in the right Vmem locations. I have set the analog out card up (F0-4AD2DA-1) using the pointers method and it is installed in slot 3 of a DL06DD.

    When trying to measure the 4-20 mA signal i get nothing with a DMM. when i connect the proportinal valve up it also doesnt respond.

    For the first scan SP0 i have:

    LD K8081 - use only output 1, and no inputs

    OUT V720 - Use Slot 3 chanel 1

    LD O3000

    OUT V721

    LD O301

    OUT V722

    and in the output part of the PID loop i have:

    LD V3005 - Control output of PID

    BCD

    OUT V2010 - output 0-4095 signal to analog card

    Does this seem correct? It all seems to be working correctly on the PIC View screen!