adccommunitymod (AutomationDirect) asked a question.

F2-04RTD Problem

Created Date: June 13,2007

Created By: NitraMA

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I try to use a F2-04RTD but the only reading I have is "0 "... I connect my "omega RTD-850 " (a PT100) to the F2-04RTD like this : RTD + ---- > CH1+ RTD - ---- > CH1- RTD Ground ---- > COM I try 3 RTD to be sure that is not a hardware problem. It seem pretty simple, but I don't know where is my mistake. The jummpers on the card is ok Ladder: I do what I found in the D2Analog PDF I use the slot 2 (the 3nd after the CPU slot) at the first scan LD K400 OUT V7662 LDA O2000 OUT V7672 and V2000-V2001 still at "0 " Thanks for your help


  • adccommunitymod (AutomationDirect)

    Created Date: June 13,2007

    Created by: FACTSTech

    Time to break out the ohm meter and measure the RTD, you should be able to read 100 ohms. One set will read 0 ohms this will wire to (-) and the other to COM. The 100ohm lead then wires to (+).

  • adccommunitymod (AutomationDirect)

    Created Date: June 13,2007

    Created by: NitraMA

    I try to use a F2-04RTD but the only reading I have is "0 "... I connect my "omega RTD-850 " (a PT100) to the F2-04RTD like this :

    RTD + ----> CH1+

    RTD - ----> CH1-

    RTD Ground ----> COM

    I try 3 RTD to be sure that is not a hardware problem. It seem pretty simple, but I don't know where is my mistake.

    The jummpers on the card is ok

    Ladder:

    I do what I found in the D2Analog PDF

    I use the slot 2 (the 3nd after the CPU slot)

    at the first scan

    LD K400

    OUT V7662

    LDA O2000

    OUT V7672

    and V2000-V2001 still at "0 "

    Thanks for your help

    Expand Post