hey guys i got another one for ya's ,, how do i keep settings incase of a power loss,,i want to be able to store custom times and allready set internal coils. if i get a battery will my plc hold these settings or do i need to do something else. what benifits does the battery have over the cap? i know the cap will die after a few days or so but is there anything else? so here is what happens, when i simulate a power loss i have to go into my hmi and set up all my set times and contacts but if im away and i lose power i will not be able to reset these settings.. thanks


  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: milldrone

    hilltop,

    In Direct soft, PLC, setup, retentive ranges, you can change or confirm what the retentive ranges for your particular plc. The super capacitor will hold these values for a couple of days. the battery is avalible at the ADC website D2-BAT-1

    DL06, D2-250(-1), D2-260, D3-350 CPUS & C-MORE TOUCH PANEL BATTERY

    Over at plcs.net Ron Beufort has a discussion abot retentive coils http://www.plctalk.net/qanda/showthread.php?p=71786&postcount=1

    Here are some threads about non volatile memory http://forum1.automationdirect.com/board/Forum1/HTML/001054.html http://forum1.automationdirect.com/board/Forum1/HTML/001712.html http://forum1.automationdirect.com/board/Forum1/HTML/002624.html http://forum1.automationdirect.com/board/Forum1/HTML/002725.html

    Vaughn

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: Bob S BN

    Install the battery for much longer memory retention. Check the manual for special relays that can indicate low battery on your HMI. In directsoft, go to menu PLC>setup>retentative ranges to choose what memory segments you want retained during power down.

  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: marksji

    The cap holds re-tentative memory for a couple of days at best.

    The battery will hold re-tentative memory for a real long time... in my experience the battery will last several years.

  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: Rich19551

    MMMMMMM I wonder where you put the battery for an 05 and 06

  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: chris.zeman

    I think the battery holder for the 06 is on the front near Port 2, but I don't have one in front of me at the moment to verify that.

    The 05 doesn't have a battery holder. I'm pretty sure you have to buy that memory cartridge.

    Chris

  • adccommunitymod (AutomationDirect)

    Created Date: May 10,2007

    Created by: milldrone

    Rich19551,

    On an 06, the battery is located above the status leds. Chris.Zeman is right the 05 requires a memory cartrige D0-01MC. Which also happens to use the same battery inside.

  • adccommunitymod (AutomationDirect)

    Created Date: May 09,2007

    Created by: hilltop

    hey guys i got another one for ya's ,, how do i keep settings incase of a power loss,,i want to be able to store custom times and allready set internal coils. if i get a battery will my plc hold these settings or do i need to do something else.

    what benifits does the battery have over the cap? i know the cap will die after a few days or so but is there anything else? so here is what happens, when i simulate a power loss i have to go into my hmi and set up all my set times and contacts but if im away and i lose power i will not be able to reset these settings.. thanks