adccommunitymod (AutomationDirect) asked a question.

0 - 7 Volts Discrete Input

Created Date: April 26,2007

Created By: yura

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Can anyone help me with the problem? I have an ultrasonic detector. Signals are discrete - 0 - nothing( "0 "), +7V - something( "1 "). Is there any "normalizer " to connect to my DL06 onboard inputs ( "0 - 1 " sensitivity edge is 10.8V)?


  • adccommunitymod (AutomationDirect)

    Created Date: April 26,2007

    Created by: KPrice

    yura, There would be a number of ways to do this, but I'm not finding any off-the-shelf devices. Solid-State Relays, large input voltage range(3.5-32VDC) to handle your 7V, but you would need to add resistance across your input to assure turn-off. Coil-type relays would handle the PLC input, but you would need to add resistance in series with the coil to reduce your 7V down to the 6V coil rating. I haven't seen any voltage-sensing relays with the drop-out range adjustable down to your 7V. Hope this gives some more ideas.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 26,2007

    Created by: yura

    Can anyone help me with the problem? I have an ultrasonic detector. Signals are discrete - 0 - nothing( "0 "), +7V - something( "1 "). Is there any "normalizer " to connect to my DL06 onboard inputs ( "0 - 1 " sensitivity edge is 10.8V)?