adccommunitymod (AutomationDirect) asked a question.

New to DirectSoft, DI help needed

Created Date: April 12,2007

Created By: NHtech

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello, I put together a dl205 rack with a DL240 cpu Slot 0: 8-ch analog in (current) Slo1 1: 32 DI, Slot 2, 32 DO I wired up the D2-32ND3 cards with Ziplink cable and Ziplink module (ZL-CM40) I have a simple level switch, I wire it in (A0 - Switch - 24v+, 24v- - Com 1 (both Com 1) When I toggle the switch in run mode with data view and ladder watch on, I see no changes! I have worked with DL06's before and never had this problem. Is this a source/sink issue? Do I have the wrong wiring? I am referencing the DL205 user manual Rev A 8/03 section 2-31 I can get my outputs to fire no problem... any help appreciated!


  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: FACTSTech

    What firmware version is in your DL240 CPU?

    The latest is V. 3.3 .

    Is the level switch just a contact? If so you cannot switch 24V directly into the analog channel input, this will destroy the input. You will need approx. 950 ohms in series to generate 20mA from 24V source.

  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: NHtech

    Firmware is 3.3

    I am trying to get my DI to respond, not the AI.

    I put X0 in Directsoft and it's state does not change. On the DL06 at least I had indicator lights, but on the 205 I don't.

    I wired the ziplink terminal block according to the instruction diagram. I have 24v going through the switch, verified with multimeter, and no response on the PLC/DirectSoft.

    Any ideas? Thanks

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: FACTSTech

    A F2-08AD-1 or F2-08AD-2 will occupy 16 X's so the first input reference on your 32 point DI will be X20.

  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: FACTSTech

    .

  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: NHtech

    Wow, simple and effective! Don't know where I missed that in the manual, but thanks!

    Is this the only module with a starting address that's not zero?

    Thanks again!!!!!

  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: NHtech

    After further study, I see that prior slots will affect the starting address.

    Since My DO is the first output card, does this mean it's first address is Y0? and if I had a second DO, it's first Y address is octally, one in addition to the prior card's limit (ie Y33)?

    Thanks

  • adccommunitymod (AutomationDirect)

    Created Date: April 12,2007

    Created by: NHtech

    Hello,

    I put together a dl205 rack with a DL240 cpu

    Slot 0: 8-ch analog in (current)

    Slo1 1: 32 DI, Slot 2, 32 DO

    I wired up the D2-32ND3 cards with Ziplink cable and Ziplink module (ZL-CM40)

    I have a simple level switch, I wire it in (A0 - Switch - 24v+, 24v- - Com 1 (both Com 1)

    When I toggle the switch in run mode with data view and ladder watch on, I see no changes! I have worked with DL06's before and never had this problem.

    Is this a source/sink issue?

    Do I have the wrong wiring? I am referencing the DL205 user manual Rev A 8/03 section 2-31

    I can get my outputs to fire no problem...

    any help appreciated!

    Expand Post