adccommunitymod (AutomationDirect) asked a question.

PT1000 RTD with F0-04AD-1

Created Date: December 13,2006

Created By: Leviathon

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am new to controls so please bear with me. I have spent tiring hours trying to understand how to setup a PT1000 RTD with the F0-04AD-1 12-bit analog input module. What will the RTD field circuit have to look like in order to operate acurately in a range from -40°F to 100°F (approx. 843-1147 ohms)using the 4-20 mA input on the module? Any advice or links to resources would be greatly appreciated. Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: Tech Guy

    You will need a FC-R1 signal conditioner to get an RTD transformed to 4-20ma.

  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: Leviathon

    Would I need a signal conditioner for a 0-10VDC (instead of 4-20 mA)Analog Input module as well?

  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: FACTSTech

    If changing modules is an option, the best solution would be to get a F0-04RTD. The F0-04RTD is designed for RTD input and gives a direct temperature reading.

  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: Leviathon

    How about a bridged RTD used in conjunction with an F0-04AD-2? Has anyone ever used a setup like that?

  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: Tech Guy

    The only way that this is going to work is to get a F0-04RTD or a FC-R1 or the equivalent.

  • adccommunitymod (AutomationDirect)

    Created Date: December 15,2006

    Created by: FACTSTech

    How about a bridged RTD used in conjunction with an F0-04AD-2? Has anyone ever used a setup like that?

    You will need a very precision reference power supply, several resistors to setup as voltage divider, being careful not to run to much current through the RTD. This will cause all of your reading to be off in temperature. Then you will need an intensive ladder program to compensate for the not linear effects of the resistance changing over the temperature scale.

    By the time you get done messing around with all of this......will be cheaper to use the RTD module since all of this is built in...Expensive we are the least of ALL the PLC products on the market.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 13,2006

    Created by: Leviathon

    I am new to controls so please bear with me. I have spent tiring hours trying to understand how to setup a PT1000 RTD with the F0-04AD-1 12-bit analog input module. What will the RTD field circuit have to look like in order to operate acurately in a range from -40°F to 100°F (approx. 843-1147 ohms)using the 4-20 mA input on the module? Any advice or links to resources would be greatly appreciated.

    Thanks

    Expand Post