adccommunitymod (AutomationDirect) asked a question.
comparative contacts (easy question)
Created Date: June 09,2005
Created By: jeremyvance
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I'm trying to compare a timer's current value to a constant (if TA2 is >= 3 seconds do this...). I'm using a DL06. Can someone please help me.
Created Date: June 09,2005
Created by: jeremyvance
I'm trying to compare a timer's current value to a constant (if TA2 is>= 3 seconds do this...). I'm using a DL06.
Can someone please help me.
Created Date: June 09,2005
Created by: bcarlton
You should be able to do that. The right side must be either a V register or a constant. An example of this using your instance would be TA2>= K30 (because standard timers have 1/10th second resolution).
Created Date: June 10,2005
Created by: franji1
What's good about the relationals on timer/counter accumulators and K values is that the accumulators are BCD and the K values are BCD/HEX. So when you do
TA2 K30
--]>= [--
you really are comparing the accumulator to the value 30.
Created Date: June 10,2005
Created by: jeremyvance
Thanks guys, I had it reversed because the logic really needed to be less than. Thanks!
Created Date: June 10,2005
Created by: bcarlton
Ah - you found out that constants (K) are not permitted on the left side.
Created Date: June 10,2005
Created by: elevmike
Originally posted by bcarlton:
Ah - you found out that constants (K) are not permitted on the left side.
I guess I must have been lucky. I never realized this.
Created Date: June 13,2005
Created by: marksji
Originally posted by elevmike:
I guess I must have been lucky. I never realized this.
News to me too... and I use a BUNCH of compares... Guess it just never came up.
Created Date: June 14,2005
Created by: jeremyvance
thanks guys for the help. Works great. I guess I'm not the only one who learned something here. http://forum1.automationdirect.com/board/smile.gif