adccommunitymod (AutomationDirect) asked a question.

Analog Input PLC Scaning

Created Date: June 07,2005

Created By: carane

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hi, i'm using the pointer method to scale 16 analog inputs with a DL-260 CPU. If the CPU is reading 4 channels in one scan, how can i do to read the next 4 channels and the other channels on the next scan? Thanks a lot.


  • adccommunitymod (AutomationDirect)

    Created Date: June 07,2005

    Created by: carane

    Hi, i'm using the pointer method to scale 16 analog inputs with a DL-260 CPU.

    If the CPU is reading 4 channels in one scan, how can i do to read the next 4 channels and the other channels on the next scan?

    Thanks a lot.

  • adccommunitymod (AutomationDirect)

    Created Date: June 07,2005

    Created by: Tech Guy

    When you are using the pointer method, there really isn't anything you can do to modify it. The PLC will read the analog inputs the best and fastest way that it can.

  • adccommunitymod (AutomationDirect)

    Created Date: June 07,2005

    Created by: carane

    Yes, it's correct, but i'm trying to read a thermocouple module and the DL-260 CPU can read only 4 channels per scan. When does the PLC read the next 4 Channels? (i have 16 thermocouple signals)how can i programing that?

  • adccommunitymod (AutomationDirect)

    Created Date: June 07,2005

    Created by: bcarlton

    With 16 thermocouples you have 4 cards. Are you asking if the CPU reads 4 channels from one card, then on the next scan reads 4 channels from the next card etc? I think probably the CPU reads all 4 channels from each card on each scan. I think you are confusing the contrast with a DL230's operation which can only process one channel from each card per scan.

  • adccommunitymod (AutomationDirect)

    Created Date: June 07,2005

    Created by: carane

    Yes, i would like to know if the CPU reads all channels in one scan, i mean the 16 channels (4 channels by card) in one scan or if it reads 4 channels in one scan and the other 4 channels in the next scan, because the manual only explain that the CPU reads 4 channels per scan.

    Thanks a lot.

  • adccommunitymod (AutomationDirect)

    Created Date: June 08,2005

    Created by: Tech Guy

    The manual explains the behaviour as if there were only one card. Unless specified otherwise, each card is handled in exactly the same manner.

    So if the manual says that you read 4 channels of a card in each scan, it is refering to each individual card. It doesn't change regardless of how many cards you have.

    If you have 4 cards then it will read 4 channels from card 1, 4 channels from card 2, 4 channels from card 3, and 4 channels from card 4 on each scan.

    Expand Post